Saturation test of a 1500/5 multi-ratio CT
    During a saturation test of a 1500/5 multi-ratio CT, 400 volts is applied to the X1 to X4 tap. The X1 to X4 tap is the 1200/5 ratio. What is the expected voltage across the X1 to X5 tap?
    Correct answer is 0 Volts.
    Can we have clarification on what the question is suggesting? Are you applying 440 V directly on the taps? Aren't the X4 and X5 taps the same point, electrically, and would therefore have the same potential voltage?
    Mar 2016
    Quote Originally Posted by Tseppish View Post
    The 0V is the correct answer.
    The CT is not like an "autotransformer". The circuit is closing thru x1-x4. There is no current flowing on X5. So zero current = zero voltage.
    307
    Quote Originally Posted by nscdrgs View Post
    Agreed. This question has kind of tricky wording.
    During saturation test, Multi-tap CT is an autotransformer
    The voltage across X1-X5 in the condition described will be 500V. 1500/1200 X 400 = 500
    Apr 2017
    CT Testing
    Attached Files Attached Files
    I don't follow? If you have voltage applied across terminals 1 and 4 of an autotransformer winding, even if there is no current flowing at terminal 5 you would still measure a boosted voltage.
    What is different about a CT winding?
    I actually tried this because it didn't make sense to me:
    200/400/600:5 CT.
    I applied 5VAC to X1 and X2 and got 15VAC between X1 and X4, just like you would expect on any multitap winding.
    Maybe I'm missing something, but it appears that test answer is incorrect.
    Feb 2019
    500V is the answer
    GPerske and BigJohn are correct.
    The entire length of the coil is one continuous wire. Therefore regardless of where you stab into the taps with your test voltage, voltage will exist on the entire coil and will be boosted beyond the test points, all the way to each end of the coil.
    1500/1200x400=500.
  1. What is the turns ratio?
    By franko26 in forum NETA Level 2 Exam
    Last Post: July 10, 2018, 03:41 PM
  2. Problem running ratio test with Megger multitap CT test set
    By ejbrewer in forum Electrical Testing Talk
    Last Post: June 30, 2016, 03:13 AM