Which would achieve a 120/69V secondary voltage?
13. On a given 480/277V system, which of the following would be used to achieve a 120/69V secondary voltage?
Your Answer: (3) 4:1 PTs connected Delta-Delta
Correct Answer: (3) 4:1 PTs connected Wye-Wye
Robert0
3 PTs connected Delta-Delta with a Turns Ratio of 4:1 will get you close to the result of 120/69V but not close enough. The problem with this configuration is that the Line-to-Line voltage and Winding voltage will both be 120V. We need the Winding voltage to be 69V. You need a Wye-configuration on the secondary to achieve this. When you use 3 PTs connected Wye-Wye with a Turns Ratio of 4:1, you get a Line-to-Line voltage of 120V and a winding voltage (can be called Line-to-Neutral in a wye configuration) of 69V.
If you see a system described in terms of 2 voltages like 120/69V, it's likely a a wye configuration. You can check this by dividing the smaller voltage into the bigger voltage. The result will be 1.732...
If only one voltage is given, odds are it's a delta.
Robert0
Acronym WiDe works really well here. For Wye configuration current (I) is equal between phase and line. For Delta configuration voltage (E) (Electromotive force, which is measured in Volts (V)) is equal between phase and line. (phase to ground and line to line)
For Wye configuration, Line Voltage = sqrt (3) * Phase Voltage (ex: Line Voltage = 277 * 1.732 = 480)
For Delta configuration, Line Current = sqrt (3) * Phase Current
sqrt(3) ~ 1.732
By RGarcia in forum NETA Level 2 Exam
Last Post: November 7, 2021, 08:41 PM
By bec51392 in forum Electrical Testing Talk
Last Post: October 28, 2021, 12:00 PM
Last Post: January 31, 2021, 10:26 AM
By alexlounsbury in forum P&C / Relay Testing Talk
Last Post: November 20, 2019, 06:21 PM
By AlexT90 in forum Electrical Testing Talk
Last Post: March 18, 2018, 08:29 PM