Page 2 of 2 FirstFirst 12
Results 11 to 18 of 18
Am I missing something here? Is the right answer here? If so can someone explain?
    #11
    Jun 2021
    Houston,TX
    26
    That's what I thought
    I was trying it the way you described because that's what I had been taught. And like we have figured out it is not an answer choice. And yes it was from the pool of questions in my NETA 2 Practice Test. Unfortunately I think the question is ignoring the 4-20mA and treating it like a 0-20mA because of the answer choices available.
    I think ya'll have a slight conceptual misunderstanding of how transducers work. Transducer typically output range of 4mA to 20mA. That means 4mA equals the low range minimum, and 20mA is high range maximum. For a 0-150A CT, 4mA is equal to 0A and 20mA is equal to 150A.
    So, I've always just made my range 0mA to 16mA, with my reading minus 4.
    So, at 14mA, my calculation would be (10mA*150A)/16mA = 93.75, so my guess would be the answer of 90A due the possibility of inaccurate.
    Not sure if this question is the best example to work off of, did you get this from the question bank? Might be one to bring up to the administrators.
    To check my work I use calculators similar to this one:
    https://www.sensorsone.com/4-20ma-to...&olo=0&ohi=150
  2. #12
    Jul 2020
    Washington, United State
    44
    Quote Originally Posted by cnowak View Post
    same answer.
  4. #13
  5. bec51392 is offline NETA Level III Pro Subscriber
    Dec 2019
    Richmond VA
    51
    Sooo testguy says 105 is right, are we voting this one wrong?
  6. #14
  7. testguy's Avatar
    testguy is offline Administrator Administrator
    Apr 2010
    555
    Quote Originally Posted by bec51392 View Post
    Thanks for reporting, this question will be updated. See answer explination by Kalbi_Rob: https://testguy.net/threads/8410-Am-...4735#post14735
  8. #15
  9. bec51392 is offline NETA Level III Pro Subscriber
    Dec 2019
    Richmond VA
    51
    I took my NETA 3 this week and this question ended up on my test! Thanks to you guys I think its fair to say I got it right. Thanks everyone!
  10. #16
    Feb 2015
    Red Oak TX
    26
    CT ratio
    A 4-20mA single CT has a max range of 150 amp what is the amps at 14mA?
    140A
    105A
    150A
    90A
    105A
    150 divided by 20 is 7.5
    That would be 7.5mA on secondary per 1 amp on primary.
    at 14mA on secondary (14 x 7.5 = 105) that would be 105 amp on primary.
    Ignore the 4 in the 4-20mA range as that is just a pickup for accuracy. Even using on 16 or 17 for the span of the range of the 4-20mA, the answer would be 123A or 131A, which is not an option, so the A per mA ratio is based on the 150 divided by 20 and ignores the lower limit of 4.
  12. #17
    Feb 2015
    Red Oak TX
    26
    low limit
    Using that calculator with 30 as the Low Limit, it calculates the primary current to be 105A.
  14. #18
  15. Jamo33 is offline Junior Member Pro Subscriber
    Jun 2021
    Quote Originally Posted by BruceG400 View Post
    If this is a transducer, then at 0 amps the output will be 4mA.
    So, rather than the lower limit being 30A by calculating 150A/20mA as the max outputs, we are instead calculating 150A/(20-4) to adjust for the 4mA offset. So it is instead 150/16=9.375mA per primary Amp
    Then use this reading and multiply it by the corrected secondary reading ie (14mA-4mA)=10
    9.375*10=93.75A
  1. Ground fault current on neutral resistor
    By MrBolt in forum NETA Level 2 Exam
    Last Post: November 6, 2021, 06:54 PM
  2. Can someone explain meter accuracy?
    By RGarcia in forum NETA Level 3 Exam
    Last Post: February 2, 2021, 08:13 PM