Results 1 to 6 of 6
200kv circuit breaker withstand test advice
  1. tcoupekyle is offline Member Pro Subscriber
    Aug 2021
    Gonna use a 200kv Phenix hi pot to test done high voltage breakers.
    Any advice?
    Haven't started yet but never used one this large.
  3. tcoupekyle is offline Member Pro Subscriber
    Aug 2021
    Quote Originally Posted by tcoupekyle View Post
    Any advice?
    https://share.icloud.com/photos/073R...u_0co16_tM6Uow
    Any advice?
    Sounds like fun, make sure you are meeting the clearance requirements and using corona suppression. Lastly, be safe and try to minimize the light show.
    16
    Any advice?
    If the set trips off it may not necessarily be the device your testing.
    If you have an issue: (Maximum output is 50mA) I believe. Keep your output lead as short and as corona free as possible. You may have to get creative if there is to much leakage current. Such as wrapping 10awg wire around 2" dia PVC pipe to create a output lead that looks like a "Slinky" or use a pipe or 4" laundry duct to make the connection to cut down on leakage. An AC test set only has so much power available so leakage should be as minimal as possible. Depending on your test specs also keep an eye on your duty cycle.
    You may get lucky and just hook it up and be good to go.
  9. tcoupekyle is offline Member Pro Subscriber
    Aug 2021
    Quote Originally Posted by TestTech View Post
    Right on guys, I'll let you know how it turns out
  11. tcoupekyle is offline Member Pro Subscriber
    Aug 2021
    Well easy peasy. No issues. Ran a bare copper to the specimen and tied other poles to ground with bare copper and ramped it up to 200kv for 5 minutes no problem.
    Thanks all
  1. Circuit Breaker Simulator
    By evan003 in forum P&C / Relay Testing Talk
    Last Post: November 6, 2021, 06:05 PM
  2. Eaton RGH65K circuit breaker ground fault test
    By Misae1 in forum Electrical Testing Talk
    Last Post: November 24, 2020, 08:48 PM
  3. Copper cable short circuit current withstand
    By J2019L in forum NETA Level 4 Exam
    Last Post: April 25, 2019, 10:13 AM
  4. Ground fault pickup test for 120V GFCI circuit breaker (How-to)
    Last Post: August 9, 2017, 08:18 PM
