    VLF on 35kV cable won't start while one phase is connected to MV transfomer

    While conducting MV cable acceptance testing at 44kV using an HVA60, it was found that the test would not start while one of the phases was connected to the MV transformer (B phase) with the transformer load break switch open.
    All cables did fine on DC insulation resistance and the transformer passed all acceptance testing. Still, until the B phase dead breaks were lifted from the transformer, the VLF would not start in this particular instance. This was just one of approximately sixty transformers on site, so it was very unusual. The cables tested fine (VLF) once they were un-landed.
    Has anyone experienced this?