VLF Dead break terminations

 Jump to latest post
Page 2 of 2 FirstFirst 12
    #11
  1. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member
    Join Date
    Feb 2018
    Location
    Jacksonville, NC
    Posts
    244
    Reputation
    Quote Originally Posted by tcoupekyle View Post
    Hey! Yeah that's what we decided to do build another and a stress cone to try it.
    That's exactly what we been looking for. Is that how you normally test these?
    I've always just used the half splice and hadn't had issue until now. But maybe in the past it was all lower voltage. In Maintenance situations.
    We found around 37-42 KV (based on weather) open Pass-Thru Bushings start to arc. That was before we learned (like you are now) that we needed to produce a proper rig to test.
    We contracted a MV splicer to create 3 ft t-body cables and put lug terminals at the other end for our cable connections, since we could easily attach corona suppression balls on the end along with our test cable.

  2. #12
  3. Join Date
    May 2017
    Posts
    8
    Reputation
    Quote Originally Posted by Kalbi_Rob View Post
    We found around 37-42 KV (based on weather) open Pass-Thru Bushings start to arc. That was before we learned (like you are now) that we needed to produce a proper rig to test.
    We contracted a MV splicer to create 3 ft t-body cables and put lug terminals at the other end for our cable connections, since we could easily attach corona suppression balls on the end along with our test cable.
    Exactly.

    In addition, its important to keep the various test rigs that you make clean and in good shape. You dont want to remove a customers new clean silicone coated T-Body and plug in a test jig that has been rolling around the back of your van for a month with dirt and sand stuck in the used silicone. It may pass the your VLF test but certainly wont last as long at it should when you plug the now dirty new T-Body into the transformer or switch after your done.

  4. #13
  5. tcoupekyle is offline Junior Member Pro Subscriber
    Join Date
    Aug 2021
    Posts
    15
    Reputation
    Quote Originally Posted by Kalbi_Rob View Post
    We found around 37-42 KV (based on weather) open Pass-Thru Bushings start to arc. That was before we learned (like you are now) that we needed to produce a proper rig to test.
    We contracted a MV splicer to create 3 ft t-body cables and put lug terminals at the other end for our cable connections, since we could easily attach corona suppression balls on the end along with our test cable.
    Thanks!

  6. #14
  7. tcoupekyle is offline Junior Member Pro Subscriber
    Join Date
    Aug 2021
    Posts
    15
    Reputation

    Finished

    We built a test rig similar to what you pictured. And testing went ultimately very well.
    Thank you all so much.

Page 2 of 2 FirstFirst 12
Subscribe

Login or register to leave a reply!


Share this thread

Related Topics

  1. It's not Dead till you Prove it's Dead!!!
    By marvinray in forum Safety and Arc Flash Talk
    Replies: 6
    Last Post: January 31, 2021, 10:30 AM
  2. Taping Medium Voltage Cable Terminations
    By RedBrick in forum Electrical Testing Talk
    Replies: 3
    Last Post: September 28, 2020, 07:39 PM
  3. Replies: 5
    Last Post: August 2, 2019, 12:58 PM
  4. What IEEE level cable terminations should be used?
    By kenner14 in forum NETA Level 4 Exam
    Replies: 1
    Last Post: October 6, 2017, 03:57 PM
  5. Danger after lockout of GE Power Break equipped with electric charge
    By SecondGen in forum Safety and Arc Flash Talk
    Replies: 0
    Last Post: April 11, 2016, 02:38 PM

Tags for this Thread



Related Content


Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support