Remembered NETA 2 Questions Help

 Jump to latest post
Page 3 of 3 FirstFirst 123
    #21
  1. Miller1085's Avatar
    Miller1085 is offline Junior Member Pro Subscriber
    Join Date
    Dec 2019
    Posts
    4
    Reputation

    NEMA 3R

    Quote Originally Posted by SecondGen View Post
    This could be b, c, or d but NEMA 4 would offer the most protection.

    https://testguy.net/content/158-NEMA...ical-Equipment

    NEMA 3R enclosures are compatible for both indoor or outdoor applications and holds the least demanding rating for outdoor use.

    NEMA 3R Characteristics:

    Protection against incidental contact with enclosed equipment
    Protection from falling dirt, rain, sleet and/or snow
    Drainage provision
    Protection against rain at a level higher than the lowest live part
    Alternate locking and latching mechanisms available

  2. #22
  3. Join Date
    Apr 2018
    Posts
    50
    Reputation
    Quote Originally Posted by A_Powers1992 View Post
    To Whom it May Help:



    4.) Which XFMR test has the ability to magnetize the windings?

    a.) Power Factor
    b.) TTR
    c.) Excitiation
    d.) Zero sequence impedance


    Doble criteria my company uses states that a TTR test can magnetize the core, not windings. Excitation testing is to be performed before TTR for this reason.

  4. #23
  5. Join Date
    Jun 2021
    Posts
    5
    Reputation

    Thanks

    Thank you for the questions. Some of these I did not know either. More stuff to study I guess.

  6. #24
  7. Join Date
    Feb 2018
    Location
    Jacksonville, NC
    Posts
    246
    Reputation
    Quote Originally Posted by rofo42 View Post
    Doble criteria my company uses states that a TTR test can magnetize the core, not windings. Excitation testing is to be performed before TTR for this reason.
    Excerpt from FACILITIES INSTRUCTIONS, STANDARDS, AND TECHNIQUES, VOLUME 3-31, TRANSFORMER DIAGNOSTICS

    CAUTION:
    Perform the excitation test before any direct current (dc)
    tests. Excitation Current Tests should never be
    conducted after a dc test has been performed on the
    transformer. Results will be incorrect because of
    residual magnetism of the core left from the dc tests.
    DC WINDING RESISTANCE MEASUREMENT is the largest DC test performed on the transformer. TTR and IR testing does not have the same power applied to cause significant magnetism.
    My practice has always been to perform Power Factor Testing before any other test. I've had arguments with techs that NETA says to perform IR test first or perform IR first to check condition of Xfmr to prevent unnecessary tests (neither I agree are important as the above caution). I've always performed winding resistance last, since that same test set has the ability to de-mag the XFMR.

Page 3 of 3 FirstFirst 123
Subscribe

Login or register to leave a reply!


Share this thread

Related Topics

  1. NETA 4 exam questions I am unsure about
    By mmacdonell in forum NETA Level 4 Exam
    Replies: 2
    Last Post: August 6, 2021, 07:15 AM
  2. NETA 4 Exam Questions 7/2018
    By MartyCoyne in forum NETA Level 4 Exam
    Replies: 28
    Last Post: February 25, 2021, 12:27 PM
  3. Why so few questions for NETA 4 exam?
    By mmacdonell in forum NETA Level 4 Exam
    Replies: 3
    Last Post: February 10, 2020, 12:14 PM
  4. Challenging NETA questions after the test
    By adamstraub in forum NETA Level 3 Exam
    Replies: 1
    Last Post: October 24, 2019, 07:38 AM
  5. Couple NETA III Questions
    By jaycee91 in forum NETA Level 3 Exam
    Replies: 1
    Last Post: January 23, 2019, 01:14 PM

Tags for this Thread



Related Content


Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support