Breaker Contact Resistance by Type
    Nov 2014
    Which of these contact resistance (in micro-ohms) readings are passing?
    A: 3200A Masterpact Breaker: A - 1252, B - 1300, C - 1171
    B: 400A Eaton Molded Case Breaker: A - 850, B - 772, C - 813
    C: 1200A VCP-W Breaker: A - 150, B - 151, C - 145
    D: 15KV GE OCB Breaker: A - 175, B - 300, C - 425
    What do you guys think? everyting seems high to me
    213
    Quote Originally Posted by adamwilson View Post
    Per NETA, there cannot be 50% difference between readings, thus you take the lowest reading and multiply by 1.5, and the highest reading cannot exceed that value.
    D is failing since 175*1.5=262.5, and both b and c are higher than 262.5
    As a general look, A, C and D look abnormally high with regards to expected readings, but in spec per NETA.
    440
    Agree that D looks pretty bad and the others are really high. Just knowing from experience that those specific breakers are way out of normal range, except maybe the molded case. I'd probably write up A and C as well in the real world.
    Question could probably use some language that specifies NETA. If I wasn't going off NETA, all would probably fail by my standards, except the molded case, making my answer B.
    Apr 2021
    Thank you for the informative reply, I feel like I have come across this type of questions before, and now I know what to look for.
  1. Contact resistance tester doesn't display any reading
    Last Post: December 21, 2020, 01:32 PM
  2. Replies: 8
    Last Post: August 16, 2020, 02:49 PM
  3. Expected contact resistance measurement based on breaker frame size
    Last Post: July 11, 2020, 03:01 PM
  4. Contact resistance test producing CT secondary current
    By alexlounsbury in forum P&C / Relay Testing Talk
    Last Post: November 20, 2019, 06:21 PM
  5. VCB Contact Resistance
    By shamimkhan in forum Electrical Testing Talk
    Last Post: December 8, 2017, 10:36 AM