    Breaker Contact Resistance by Type

    Which of these contact resistance (in micro-ohms) readings are passing?

    A: 3200A Masterpact Breaker: A - 1252, B - 1300, C - 1171
    B: 400A Eaton Molded Case Breaker: A - 850, B - 772, C - 813
    C: 1200A VCP-W Breaker: A - 150, B - 151, C - 145
    D: 15KV GE OCB Breaker: A - 175, B - 300, C - 425

    What do you guys think? everyting seems high to me

  2. #2
  3. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member
    Join Date
    Feb 2018
    Location
    Richmond, VA
    Posts
    216
    Reputation
    Quote Originally Posted by adamwilson View Post
    Which of these contact resistance (in micro-ohms) readings are passing?

    A: 3200A Masterpact Breaker: A - 1252, B - 1300, C - 1171
    B: 400A Eaton Molded Case Breaker: A - 850, B - 772, C - 813
    C: 1200A VCP-W Breaker: A - 150, B - 151, C - 145
    D: 15KV GE OCB Breaker: A - 175, B - 300, C - 425

    What do you guys think? everyting seems high to me
    Per NETA, there cannot be 50% difference between readings, thus you take the lowest reading and multiply by 1.5, and the highest reading cannot exceed that value.

    D is failing since 175*1.5=262.5, and both b and c are higher than 262.5

    As a general look, A, C and D look abnormally high with regards to expected readings, but in spec per NETA.

  4. #3
  5. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    448
    Reputation
    Quote Originally Posted by Kalbi_Rob View Post
    Per NETA, there cannot be 50% difference between readings, thus you take the lowest reading and multiply by 1.5, and the highest reading cannot exceed that value.

    D is failing since 175*1.5=262.5, and both b and c are higher than 262.5

    As a general look, A, C and D look abnormally high with regards to expected readings, but in spec per NETA.
    Agree that D looks pretty bad and the others are really high. Just knowing from experience that those specific breakers are way out of normal range, except maybe the molded case. I'd probably write up A and C as well in the real world.

    Question could probably use some language that specifies NETA. If I wasn't going off NETA, all would probably fail by my standards, except the molded case, making my answer B.

  6. #4
  7. Join Date
    Apr 2021
    Posts
    25
    Reputation
    Quote Originally Posted by Kalbi_Rob View Post
    Per NETA, there cannot be 50% difference between readings, thus you take the lowest reading and multiply by 1.5, and the highest reading cannot exceed that value.

    D is failing since 175*1.5=262.5, and both b and c are higher than 262.5

    As a general look, A, C and D look abnormally high with regards to expected readings, but in spec per NETA.
    Thank you for the informative reply, I feel like I have come across this type of questions before, and now I know what to look for.

Subscribe

Login or register to leave a reply!


Share this thread

Related Topics

  1. Contact resistance tester doesn't display any reading
    By lnides in forum Electrical Testing Talk
    Replies: 12
    Last Post: December 21, 2020, 01:32 PM
  2. Replies: 8
    Last Post: August 16, 2020, 02:49 PM
  3. Expected contact resistance measurement based on breaker frame size
    By SecondGen in forum Electrical Testing Talk
    Replies: 6
    Last Post: July 11, 2020, 03:01 PM
  4. Contact resistance test producing CT secondary current
    By alexlounsbury in forum P&C / Relay Testing Talk
    Replies: 9
    Last Post: November 20, 2019, 06:21 PM
  5. VCB Contact Resistance
    By shamimkhan in forum Electrical Testing Talk
    Replies: 1
    Last Post: December 8, 2017, 10:36 AM

Tags for this Thread



Related Content


Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support