    NETA Level 2 exam XFMR tables

    9. What is the NETA Recommended Minimum Insulation Resistance value for a dry-type 4,160V-480V D-D transformer primary winding?
    Your Answer: 1 Gigohm
    Help: NETA Table 100.5 (2019)

    The answers were all in Gigs...1, 5, 10, 20. The cited table doesn't recommend anything beyond Megs...what am I missing?

  2. #2
  3. Join Date
    Dec 2017
    Posts
    30
    Reputation
    Quote Originally Posted by Skoivisto View Post
    9. What is the NETA Recommended Minimum Insulation Resistance value for a dry-type 4,160V-480V D-D transformer primary winding?
    Your Answer: 1 Gigohm
    Help: NETA Table 100.5 (2019)

    The answers were all in Gigs...1, 5, 10, 20. The cited table doesn't recommend anything beyond Megs...what am I missing?

    1G would be for liquid filled.
    I would recommend understand the SI units prefixes too.
    Click image for larger version. 

Name:	maxresdefault.jpg 
Views:	1 
Size:	32.1 KB 
ID:	500
    https://www.google.com/url?sa=i&url=...AAAAAdAAAAABBL

  4. #3
  5. Join Date
    Feb 2018
    Location
    Richmond, VA
    Posts
    210
    Reputation
    Quote Originally Posted by Skoivisto View Post
    9. What is the NETA Recommended Minimum Insulation Resistance value for a dry-type 4,160V-480V D-D transformer primary winding?
    Your Answer: 1 Gigohm
    Help: NETA Table 100.5 (2019)

    The answers were all in Gigs...1, 5, 10, 20. The cited table doesn't recommend anything beyond Megs...what am I missing?
    5000 Megohms is 5 gigohms. For a dry-type transformer rated 601-5000V, minimum resistance is 5000 Megohms or 5 Gigohms

  6. #4
  7. Join Date
    Feb 2021
    Posts
    1
    Reputation
    Quote Originally Posted by Skoivisto View Post
    9. What is the NETA Recommended Minimum Insulation Resistance value for a dry-type 4,160V-480V D-D transformer primary winding?
    Your Answer: 1 Gigohm
    Help: NETA Table 100.5 (2019)

    The answers were all in Gigs...1, 5, 10, 20. The cited table doesn't recommend anything beyond Megs...what am I missing?
    5,000 Megohms is 5 Gigohms .

  8. #5
  9. archieb7 is offline Junior Member Pro Subscriber
    Join Date
    Dec 2020
    Posts
    1
    Reputation
    Quote Originally Posted by Skoivisto View Post
    9. What is the NETA Recommended Minimum Insulation Resistance value for a dry-type 4,160V-480V D-D transformer primary winding?
    Your Answer: 1 Gigohm
    Help: NETA Table 100.5 (2019)

    The answers were all in Gigs...1, 5, 10, 20. The cited table doesn't recommend anything beyond Megs...what am I missing?
    5 Gig.

Subscribe

Login or register to leave a reply!


Share this thread

Related Topics

  1. Replies: 2
    Last Post: 3 Weeks Ago, 04:03 AM
  2. How to best prepare for Neta Level 2 exam?
    By electricity in forum NETA Level 2 Exam
    Replies: 4
    Last Post: July 28, 2019, 08:20 AM
  3. Passed NETA Level 2 Exam 11/5/18
    By E-DivMafia in forum NETA Level 2 Exam
    Replies: 2
    Last Post: December 21, 2018, 07:15 PM
  4. Passed NETA Exam Level 2 11/7/18
    By Jtryon1 in forum NETA Level 2 Exam
    Replies: 2
    Last Post: November 8, 2018, 09:07 PM

Tags for this Thread



Related Content


Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support