Ground fault current on neutral resistor
A given 4160V 3-phase wye connected system is grounded by a 12 ohm resistor, what would the ground fault current be limited to? the Answer is 200A but I don't understand how?
-

Originally Posted by
MrBolt
A given 4160V 3-phase wye connected system is grounded by a 12 ohm resistor, what would the ground fault current be limited to? the Answer is 200A but I don't understand how?
What was your answer and why?
-

Originally Posted by
MrBolt
A given 4160V 3-phase wye connected system is grounded by a 12 ohm resistor, what would the ground fault current be limited to? the Answer is 200A but I don't understand how?
The key takeaway here is that it is a wye connected system.
-

Originally Posted by
SecondGen
What was your answer and why?
4160/12=346.66
-

Originally Posted by
MrBolt
4160/12=346.66
That would be correct if it was a delta system. In a wye, you must divide by the square root of three and then your resistor.
-

Originally Posted by
MrBolt
4160/12=346.66
As others have stated, the key is to use phase to ground voltage.
-

Originally Posted by
MrBolt
A given 4160V 3-phase wye connected system is grounded by a 12 ohm resistor, what would the ground fault current be limited to? the Answer is 200A but I don't understand how?
4160/1.732=2401
2401/12=200
Subscribe
Related Topics
-
By AlexT90 in forum NETA Level 3 Exam
Replies: 6
Last Post: September 13, 2020, 07:18 PM
-
By Trevorvaligura in forum NETA Level 3 Exam
Replies: 1
Last Post: February 18, 2020, 07:12 AM
-
By rynomite in forum NETA Level 3 Exam
Replies: 3
Last Post: August 2, 2019, 01:25 PM
-
By bwillsey88 in forum Electrical Testing Talk
Replies: 2
Last Post: May 18, 2017, 10:32 AM
-
By trhea@saberpower.com in forum NETA Level 3 Exam
Replies: 6
Last Post: January 8, 2016, 11:14 AM
Tags for this Thread