Wye-delta transformer secondary line current

    #1
  1. Join Date
    Dec 2020
    Posts
    8
    Reputation

    Wye-delta transformer secondary line current

    A wye-delta transformer has a turns ratio of 2:1. It has a secondary line voltage of 480 V. The secondary is connected to a wye-connected three-phase resistive load of 50 ohms in each phase. How much is the secondary line current?

    My answer is 9.6 Amps, I used 480V since it wont matter in the delta side (V line = V phase) and divide 50 ohms from it resulting 9.6 amps, however I got the question wrong. I know I line = 1.73 * I phase. I cant remember how to solve for it.

  2. #2
  3. Join Date
    Dec 2020
    Posts
    8
    Reputation

    NETA Level 2 Practice Exam

    a watt-hour meter has a watt-hour constant, kh, of 1.2 it is used with 1200/5 ratio current transformers and 14,400/120 potential transformers. what is the primary watt-hour constant kh?

    is it as simple as multiplying 1.2 by the CT Ratio and PT Ratio?

  4. #3
  5. Join Date
    Nov 2020
    Posts
    6
    Reputation
    Quote Originally Posted by RGarcia View Post
    A wye-delta transformer has a turns ratio of 2:1. It has a secondary line voltage of 480 V. The secondary is connected to a wye-connected three-phase resistive load of 50 ohms in each phase. How much is the secondary line current?

    My answer is 9.6 Amps, I used 480V since it wont matter in the delta side (V line = V phase) and divide 50 ohms from it resulting 9.6 amps, however I got the question wrong. I know I line = 1.73 * I phase. I cant remember how to solve for it.
    You have to keep in mind the connection of the load. The load is connected Wye. Take the Delta secondary voltage and convert the phase voltage into line to ground. 480V/1.732 = 277V. 277V /50 ohms = 5.54A.

Subscribe

Login or register to leave a reply!


Share this thread

Related Topics

  1. What is the line current of this transformer?
    By mattj77 in forum NETA Level 3 Exam
    Replies: 1
    Last Post: January 6, 2021, 07:12 AM
  2. Contact resistance test producing CT secondary current
    By alexlounsbury in forum P&C / Relay Testing Talk
    Replies: 9
    Last Post: November 20, 2019, 06:21 PM
  3. The power loss in a transmission line due to charging current
    By BrickSalad in forum NETA Level 4 Exam
    Replies: 0
    Last Post: July 9, 2019, 06:48 PM
  4. Cooling fans won’t stop running on transformer secondary side??
    By electrolyte in forum Electrical Testing Talk
    Replies: 1
    Last Post: October 22, 2016, 04:26 PM
  5. Important tip for measuring secondary current with AEMC PEL data logger
    By SecondGen in forum Electrical Testing Talk
    Replies: 0
    Last Post: October 8, 2015, 12:19 PM

Tags for this Thread



Related Content


Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support