Question on Ground Resistance Testing Methods
I've got a customer who needs their grounding electrodes tested for an inspection (8 electrodes total, in a 4x4 configuration). We do grounding resistance tests but typically for electrodes outside or for setting up mobile power plants, where there's plenty of room for lengthy fall-of-potential tests. The building where the electrodes are located is cramped (see picture). I'm assuming that they are all connected via a grounding grid underneath, but I will verify that once I head out there obviously. Any thoughts on the best method of testing these?
-

Originally Posted by
michaellabeit
I've got a customer who needs their grounding electrodes tested for an inspection (8 electrodes total, in a 4x4 configuration). We do grounding resistance tests but typically for electrodes outside or for setting up mobile power plants, where there's plenty of room for lengthy fall-of-potential tests. The building where the electrodes are located is cramped (see picture). I'm assuming that they are all connected via a grounding grid underneath, but I will verify that once I head out there obviously. Any thoughts on the best method of testing these?

I would perform one of two test.
First option: You can probably perform a fall-of-potential test thru the roll-up door on each ground rod.
Second option: Perform fall-of-potential test on outside of building steel, then perform 2-point test to each ground rod.
Or lastly you can perform a combination of the above, with a fall-of-potential to one ground rod, then 2-point to the other 2.
Subscribe
Related Topics
-
By madMAX in forum Electrical Testing Talk
Replies: 7
Last Post: June 27, 2018, 12:49 PM
-
By rig-electrician in forum Electrical Testing Talk
Replies: 1
Last Post: August 13, 2017, 07:56 AM
-
By iwanttotest in forum Electrical Testing Talk
Replies: 2
Last Post: February 23, 2017, 09:39 AM
Tags for this Thread
Related Content