Results 1 to 3 of 3
What is the line current of this transformer?
  1. mattj77 is offline Junior Member Pro Subscriber
    Aug 2019
    1. A given 1000kVA wye-wye transformer has a secondary rated voltage of 480/277V, what is the line current of this transformer?
    Your Answer: 3610A
    Correct Answer: 1203A
    Help: First find transformer FLA and then calculate line current.
    1. FLA = VA / L-L Voltage x 1.732
    2. Balanced Wye: Line Current = Phase Current, Line Voltage = 1.732 Phase Voltage
    I guessed the wrong answer on purpose on this one because the formula used does not fully explain how to calculate 3 power. It should actually be this:
    KVA/(3 * phase voltage)
    Why would you take the line voltage and multiply it by the sqrt(3) when it is already the product of the phase voltage * sqrt(3)?
  3. Kalbi_Rob's Avatar
    290
    Quote Originally Posted by mattj77 View Post
    Your Answer: 3610A
    Single Phase Transformer Full-Load Current (Amps)= kVA × 1000 / V
    Three Phase Transformer Full-Load Current (Amps) = kVA × 1000 / (1.732 × VL-L)
    Three Phase Transformer Available Fault Current (Amps) = kVA × 1000 / (1.732 × VL-L x %IMP)
    https://goodcalculators.com/transformer-calculator/
    To derive the equation: S (measured in VA, or KVA)
    S=sqrt(3) * V * I
    I= S/(sqrt(3) * V)
    => FLA = VA / (1.732 * V L-L)
  5. laydrive is offline Junior Member Pro Subscriber
    Oct 2019
    multiply sqrt of 3 by 480 again?
    Your Answer: 3610A
  1. transformer excitation current readings
    By kcorpuz in forum NETA Level 3 Exam
    Last Post: June 24, 2022, 12:25 PM
  2. Current Transformer Ratio and Excitation Testing
    By RedBrick in forum Electrical Testing Talk
    Last Post: September 18, 2020, 11:19 AM
  3. Transformer Primary Fault Current
    By kchenoweth in forum NETA Level 4 Exam
    Last Post: August 22, 2020, 08:46 PM
  4. The power loss in a transmission line due to charging current
    By BrickSalad in forum NETA Level 4 Exam
    Last Post: July 9, 2019, 06:48 PM
  5. Total burden on current transformer
    By Sanjayo in forum NETA Level 3 Exam
    Last Post: February 19, 2016, 01:50 PM