Follow Us
Results 1 to 3 of 3

TTR transformer that is 80% loaded

    #1
  1. Join Date
    Dec 2020
    Posts
    8
    Reputation

    TTR transformer that is 80% loaded

    What is the turns ratio of a 3-phase 500kVA, 13,200-480 volt rated delta-delta transformer that is 80% loaded

    I answered this question incorporating the 80% load into my calculation and i get 22. However it ended up being the wrong answer.

    Can someone assist me on this question.

    Thanks,

  2. #2
  3. Join Date
    Apr 2018
    Posts
    42
    Reputation
    Quote Originally Posted by RGarcia View Post
    What is the turns ratio of a 3-phase 500kVA, 13,200-480 volt rated delta-delta transformer that is 80% loaded

    I answered this question incorporating the 80% load into my calculation and i get 22. However it ended up being the wrong answer.

    Can someone assist me on this question.

    Thanks,
    The loading of a transformer doesn't effect the turns ratio. That question is seemingly giving you extra information to purposely trip you up.

  4. #3
  5. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member
    Join Date
    Feb 2018
    Location
    Richmond, VA
    Posts
    211
    Reputation
    Quote Originally Posted by RGarcia View Post
    What is the turns ratio of a 3-phase 500kVA, 13,200-480 volt rated delta-delta transformer that is 80% loaded

    I answered this question incorporating the 80% load into my calculation and i get 22. However it ended up being the wrong answer.

    Can someone assist me on this question.

    Thanks,
    80% loading is excessive information and does not affect the turns ratio.

    First information that is relevant is the transformer is delta-delta transformer, so Phase to Ground voltage = Line to Line Voltage.

    TTR= 13200/480 = 27.5