Ground defeat digitrip 1150+ on Mag Ds
what am I missing here. Can't find a defeat in any of the manuals. Secondaries don't have a ground defeat function for primary injection, I have what I thought was a ground defeat plug for the the secondary contacts with a jumper in but thats not working. I think it must just be the one for zone interlocking. I feel like I have figured this out before its just been years since i did primary on this one. Any help is much appreciated. Testing eaton magnum DS breakers with digitrip 1150+ trip units.
-

Originally Posted by
will_lunsford
what am I missing here. Can't find a defeat in any of the manuals. Secondaries don't have a ground defeat function for primary injection, I have what I thought was a ground defeat plug for the the secondary contacts with a jumper in but thats not working. I think it must just be the one for zone interlocking. I feel like I have figured this out before its just been years since i did primary on this one. Any help is much appreciated. Testing eaton magnum DS breakers with digitrip 1150+ trip units.
Ground Fault is defeated by shorting terminal B6-B7
Zone Interlock is defeated by shorting terminal B8-B9
I do not remember if it is easily seen which terminal is which, but can be difficult determining which secondary terminal is A and which is B and whether it is read from inside or outside.
-

Originally Posted by
will_lunsford
what am I missing here. Can't find a defeat in any of the manuals. Secondaries don't have a ground defeat function for primary injection, I have what I thought was a ground defeat plug for the the secondary contacts with a jumper in but thats not working. I think it must just be the one for zone interlocking. I feel like I have figured this out before its just been years since i did primary on this one. Any help is much appreciated. Testing eaton magnum DS breakers with digitrip 1150+ trip units.
B-6 to B-7
-
Thanks

Originally Posted by
will_lunsford
what am I missing here. Can't find a defeat in any of the manuals. Secondaries don't have a ground defeat function for primary injection, I have what I thought was a ground defeat plug for the the secondary contacts with a jumper in but thats not working. I think it must just be the one for zone interlocking. I feel like I have figured this out before its just been years since i did primary on this one. Any help is much appreciated. Testing eaton magnum DS breakers with digitrip 1150+ trip units.
Thank you all for your help.
Subscribe
Related Topics
-
By Kimbo Slice in forum Electrical Testing Talk
Replies: 12
Last Post: July 28, 2020, 08:27 AM
-
By cmferrer in forum Electrical Testing Talk
Replies: 2
Last Post: July 27, 2020, 08:23 PM
-
By Texron in forum Electrical Testing Talk
Replies: 2
Last Post: April 20, 2020, 06:26 AM
-
By SecondGen in forum Technical Documents
Replies: 0
Last Post: September 7, 2016, 06:49 PM
-
By keith63c in forum Electrical Testing Talk
Replies: 2
Last Post: May 25, 2016, 02:03 PM
Tags for this Thread