    Percentage Differential Mismatch

    Calculate the percentage differential mismatch for an electromechanical relay protecting a 138kV-69kV Delta-Wye 50MVA Transformer with 250:5 CTs on the primary and 500:5 CTs on the secondary, with CT ratio taps on the relay set to 5A on the high side and 9A on the low side.

    I need help with this problem, the answer is supposedly 3.78%. Thanks.

  2. #2
  3. Erased is offline Junior Member
    Join Date
    Oct 2020
    Posts
    1
    Reputation
    Quote Originally Posted by Uguessus View Post
    Calculate the percentage differential mismatch for an electromechanical relay protecting a 138kV-69kV Delta-Wye 50MVA Transformer with 250:5 CTs on the primary and 500:5 CTs on the secondary, with CT ratio taps on the relay set to 5A on the high side and 9A on the low side.

    I need help with this problem, the answer is supposedly 3.78%. Thanks.
    Now, I got a slightly different answer, so someone correct me if I'm mistaken.

    First calculate HV currents.

    Primary:
    50000000/sqrt(3)*138000 = 209.18

    Secondary:
    50000000/sqrt(3)*69000 = 418.37

    Now calculate CT currents. An electromechanical scheme on a Delta-Wye will have Wye-Delta CT's to account for the phase shift. Delta CT current must be multiplied by sqrt(3).

    Primary - Wye CT:
    209.18/50 = 4.18

    Secondary - Delta CT:
    418.37/100 = 4.18
    4.18*sqrt(3) = 7.24

    Calculate the percent mismatch as follows: On two-winding transformers,
    determine the ratio of the two relay currents and the tap values selected. The
    difference between these ratios, divided by the smaller ratio, is the percent
    mismatch.

    ((4.18/5)-(7.24/9)) / (7.24/9) = 0.0392

    3.92% with rounding errors.

    Looks like your answer came from incorrectly dividing by the larger ratio.

    (4.18/5)-(7.24/9) / (4.18/5) = 0.0377

    3.77% with rounding errors.

  4. #3
  5. Uguessus is offline Junior Member Pro Subscriber
    Join Date
    Dec 2019
    Location
    Signal Hill, CA
    Posts
    5
    Reputation
    This is awesome! Thanks a lot, Erased.

Subscribe

Login or register to leave a reply!


Share this thread

Related Topics

  1. Differential Slope 1 and 2
    By Js20981 in forum P&C / Relay Testing Talk
    Replies: 0
    Last Post: August 17, 2020, 10:30 PM
  2. Replies: 3
    Last Post: April 6, 2020, 08:54 PM
  3. Field test procedure for Modified Differential Ground Fault systems
    By Biscuit in forum Electrical Testing Talk
    Replies: 3
    Last Post: January 13, 2016, 01:39 AM

Tags for this Thread



Related Content


Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support