15kv vacuum breaker maintenance hipot test voltage
    Aug 2020
    Wondering what the test voltage is for a 15kv vacuum breaker (13.8kv nominal voltage) for AC hipot. Maintenance test. Thanks!
    237
    Quote Originally Posted by Fieldtech View Post
    First, manufacturer's do not differentiate between acceptance and maintenance test values for vacuum integrity test.
    Second, each manufacturer has a specific test voltage for each voltage rated vacuum breaker. So, to answer your question would require the manufacturer and type of breaker. My recommendation would be to look up the manual for that breaker and under vacuum integrity/withstand testing look for the appropriate voltage level.
    California
    21
    NETA has testing voltage at 27 kV for the 2019 version, but any manufacturer literature will always supersede this.
    General Electric breakers sometimes will ask for Vacuum Integrity testing at 36 kV for 10 seconds.
    Jun 2016
    Quote Originally Posted by AaronCBI View Post
    If you think about it, the contact gap is less than 1/2" on any vacuum bottle. If you apply over 10kvac across 1/2" gap that is solidly grounded on the other pole I am pretty sure it will fail.
    This is a go, no go test.
    There is no state in the real world that is a partial vacuum.
    If the bottle vacuum is compromised it will fail.
    California
    21
    Quote Originally Posted by gasman View Post
    I have tested thousands of vacuum bottles on VB1 type breakers with the ML-17 and ML-18 mechanisms at 36 kV in accordance with the manufacturer service literature. Vacuum interrupters that still have integrity to the "vacuum" will withstand this voltage for 10 seconds without failure. The contact travel for these breakers is roughly 0.55" (0.54" - 0.6" nominally).
    I have tested a few 27 kV breakers (VCP-Ws I believe) that called for over 40kV testing voltage and the vacuum interrupters were able to withstand test voltage without failure.
    Jun 2016
    Exactly what I was saying. If it is good @ 10kv, it will be good @36kv. A vacuum bottle cannot partially fail.
    Vacuum Integrity is a Pass/Fail test.
    California
    21
    Oh I am sorry, I totally misunderstood.
    Jun 2016
    Higher voltages will stress the surface leakage over the outer surface of the bottle, but if the bottle is bad it is bad.
  1. Applying a solidly grounded wire after hipot test
    By epenland in forum NETA Level 2 Exam
    Last Post: July 18, 2021, 10:13 AM
  2. Circuit Breaker voltage ratings
    By nwilliams in forum NETA Level 3 Exam
    Last Post: February 12, 2021, 07:54 AM
  3. Overpotential test voltage for low-voltage switchgear
    By AlexT90 in forum Electrical Testing Talk
    Last Post: March 18, 2018, 08:29 PM
  4. Vacuum Circuit Breaker
    By shamimkhan in forum Electrical Testing Talk
    Last Post: December 8, 2017, 10:42 AM
