What test set or method you are using for testing turns ratio on CCVTs?
    Can any of you tell me what test set or method you are using for testing turns ratio on CCVTs? Are you guys applying a high voltage to the high voltage terminal, and measuring the secondary, or are you using a test set? My understanding is a standard TTR test set will record too high of an error due to the voltage decay in the capacitor stack. Vanguard's CTV-765 seems like a simple and fast test set. Any feedback is appreciated. Thanks!
    Dec 2015
    Most simple method I think is using a power factor test set as a power supply to the HV terminal and measure the secondary voltage.
    OH/MI
    31
    Quote Originally Posted by Sanjayo View Post
    totally agree with Sanjayo, just did some a few months back, 80kv-120v I believe. we put 10kv on the high side with our omicron cpc100/td1 and measured 15v on the low side
    Could you use an AC hipot if you don't have a power factor set?
    OH/MI
    31
    Quote Originally Posted by randywright View Post
    Never tried that... not sure honestly. I don't see why not.
    Hipots usually trip out on very low levels of current.
    OH/MI
    31
    Very true. Yep, not likely you would be able to use a hipot. Good call. Depending on the ratio, I've used just a small power source.
    CCVT Ratio Test
    I personally use an M4100 to apply 10kV to the top and measuring at the bottom with a voltmeter. However, this will either be at 57 or 63 Hz, which I've recently been concerned about effecting the accuracy.
    Nov 2017
    DOBLE M4000
    Quote Originally Posted by scottxclark View Post
    We use a DOBLE M4000 power factor test set
  19. wooddy is offline Junior Member
    Jan 2018
    Quote Originally Posted by trn8ochaser View Post
  1. What is the proper formula for 3 phase turns ratio?
    By Js20981 in forum Electrical Testing Talk
    Last Post: September 5, 2020, 07:20 PM
  2. What is the turns ratio?
    By franko26 in forum NETA Level 2 Exam
    Last Post: July 10, 2018, 03:41 PM
  3. Dry Tranformer Turns Ratio
    By shamimkhan in forum Electrical Testing Talk
    Last Post: January 18, 2018, 10:22 AM