Results 1 to 3 of 3
Transformer Nameplate Help
    37
    How can I determine where H1 and H3 are located? Where would the terminal board be located?
    Thanks!
    Jun 2020
    Thanks!
    Without looking at the terminal board, you could determine where H1 & H3 are connected after doing a TTR test based upon your results.
    Aug 2015
    Transformer nameplate
    Thanks!
    Usually the bushings are H3, H2, H1 left to right when facing the primary. The nameplate will usually reference the items to the drain valve or DETC on the transformer. With a Wye secondary use the nameplate for the location of the X0 busing and then observe the opposite winding layout. Dry type transformers are not always that simple as I have discovered numerous dry type in which the layout was incorrect. In this case I followed the connections of the "middle" winding to get the correct nomenclature for the terminals.
  1. Doble Testing a Bushing: C2 reading higher than nameplate
    By Bob_Woodward in forum Electrical Testing Talk
    Last Post: April 2, 2020, 11:49 AM
  2. Neutral CT testing with no nameplate data
    By AMPPOMY84 in forum Electrical Testing Talk
    Last Post: March 15, 2020, 07:48 PM
  3. If a breaker is timing at 10 cycles slower than nameplate
    By akumaleon in forum NETA Level 3 Exam
    Last Post: February 25, 2020, 08:17 AM