    What is the turns ratio for a delta wye 138000/12470 XFMR. What is the proper formula? Thanks
  3. Kalbi_Rob's Avatar
    Richmond, VA
    187
    Quote Originally Posted by Js20981 View Post
    First step is to only use phase to ground voltages.
    For Delta, Line-to-Line = Phase-to-Ground voltages.
    For Wye, SQRT(3) * Line-to-Line = Phase-to-Ground voltages. Vp=12470/SQRT(3)=12470/1.732=7199.8V
    TTR=138000V/7200V=~19.166
    Math should be correct minus rounding errors.
  5. southbury's Avatar
    southbury is offline
    Neta 4 Tech
    Jul 2017
    as the previous post already explained
    These questions are hard to answer.
    Even NETA is vague on the exams.
    Given 138,000 to 12470
    They do not tell you the connections( I protested these questions)
    138,000 probably a line to line voltage so you would assume a delta
    12470 probably a wye voltage. 12470/square root 3=7199.56=7200
    138,000/7200=19.1666
  1. What is the turns ratio?
    By franko26 in forum NETA Level 2 Exam
    Last Post: July 10, 2018, 03:41 PM
  2. Dry Tranformer Turns Ratio