    Circuit Breaker PI Test

    Hi guys,
    I hope you all okay. I just wanted to ask do you have any excel sheet to use in Primary Injection test to see the Long time, short time values? If you have i would be glad if you share.
    Stay safe.

  2. #2
  3. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    408
    Reputation
    Quote Originally Posted by changeabilities View Post
    Hi guys,
    I hope you all okay. I just wanted to ask do you have any excel sheet to use in Primary Injection test to see the Long time, short time values? If you have i would be glad if you share.
    Stay safe.
    These values will be dependent on the specific type of trip unit you are testing but as a general reference I would recommend downloading the Utility Relay AC Pro Instruction Book for generic equations. I've included screenshots of the LT and ST formula along with a link to the original manual below, check out page 20.

    Click image for larger version. 

Name:	ac-pro-lt-st-formulas.png 
Views:	0 
Size:	158.1 KB 
ID:	459

    http://www.utilityrelay.com/PDFs/Pro...ion_Manual.pdf

  4. #3
  5. Join Date
    Jun 2018
    Posts
    13
    Reputation
    Quote Originally Posted by SecondGen View Post
    These values will be dependent on the specific type of trip unit you are testing but as a general reference I would recommend downloading the Utility Relay AC Pro Instruction Book for generic equations. I've included screenshots of the LT and ST formula along with a link to the original manual below, check out page 20.

    Click image for larger version. 

Name:	ac-pro-lt-st-formulas.png 
Views:	0 
Size:	158.1 KB 
ID:	459

    http://www.utilityrelay.com/PDFs/Pro...ion_Manual.pdf
    Thank you so much for your response.

  6. #4
  7. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    408
    Reputation
    Quote Originally Posted by changeabilities View Post
    Thank you so much for your response.
    No problem, I'd also recommend checking out the table on page 18 it will give you some expected trip times for the LT function along with allowable tolerance for various bands and test currents. Again, this may be different depending on the specific trip unit but it gives you a general idea.

    Click image for larger version. 

Name:	ac-pro-lt-table-ex.png 
Views:	15 
Size:	22.2 KB 
ID:	460

Subscribe

Login or register to leave a reply!


Share this thread

Related Topics

  1. Circuit Breaker Simulator
    By evan003 in forum P&C / Relay Testing Talk
    Replies: 12
    Last Post: April 4, 2020, 04:43 PM
  2. Vacuum Circuit Breaker
    By shamimkhan in forum Electrical Testing Talk
    Replies: 1
    Last Post: December 8, 2017, 10:42 AM
  3. Ground fault pickup test for 120V GFCI circuit breaker (How-to)
    By SecondGen in forum Electrical Testing Talk
    Replies: 0
    Last Post: August 9, 2017, 08:18 PM
  4. Phasing a Tie Circuit Breaker
    By Larry5443 in forum Electrical Testing Talk
    Replies: 27
    Last Post: July 2, 2015, 02:43 PM

Tags for this Thread



Related Content


Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support