    Two loads are connected to the same source. Load 1: 1250KVA @ 0.85PF. Load 2: 600KW, 300KVAR. What is the combined load in KVA & PF?
    Another user posted 1825.8kVA @ 0.91 PF in a different thread and I couldn't come up with this answer. Here is what I did:
    Find combined PF:
    1.) Using individual PF, calculate KW and KVAR of each load
    2.) Add KW of each load to find combined KW
    3.) Add KVAR of each load to find combined KVAR
    4.) Combined PF is calculated as:
    4a.) Tan0 = Combined KVAR / Combined KW
    4b.) Combined PF = Cos (TanInv0)
    1a) 1,062.5kW, 658.478kVAR = 1,250,000VA @ 0.85 PF
    1b) 600kW, 300kVAR = 670,820VA @ 0.8944 PF
    2.) Combined kW = 1,662,500 W
    3.) Combined kVAR = 958,478 VAR
    4a.) Tan0 = 958,478 / 1,662,500 = 0.5765281
    4b.) Cos(TanInv0.5765281) = Cos(29.9646573) = 0.8663
    Find kVA using combined values and A^2 + B^2 = C^2, then sqrt(C^2):
    1.) 1662.500^2 = 2763906.25
    2.) 958.478^2 = 918680.076484
    3.) 2763906.25 + 918680.076484 = 3682586.326484
    4.) sqrt(3682586.326484) = 1,919.006
    Result: 1,919kVA @ 0.87PF
    Can someone check my work and let me know if I'm doing something wrong? I was able to verify my combined values using this calculator: https://www.omnicalculator.com/physics/power-factor
    Original thread: https://testguy.net/threads/5088-NET...estions-1-2017
  2. #2
  3. driftmy240 is offline Junior Member Pro Subscriber
    Join Date
    Oct 2017
    Posts
    1
    Reputation
    Quote Originally Posted by SecondGen View Post
    Find combined PF:
    I calculated it two different ways and got the same answer you did.
    Load 1 + Load 2 = 1,919kVA, PF=0.87
Subscribe
Login or register to leave a reply!
Share this thread
Related Topics
  1. Full-load current for single-phase AC motor
    By test11 in forum NETA Level 2 Exam
    Last Post: June 17, 2020, 11:45 AM
  2. Load tap changer location
    By Achandler in forum Electrical Testing Talk
    Last Post: May 20, 2020, 09:05 AM
  3. Switching under full load.
    By TrapFlyVenus in forum Safety and Arc Flash Talk
    Last Post: April 20, 2020, 02:16 PM
  4. Replies: 0
    Last Post: January 16, 2020, 02:18 PM
  5. Load currents in an alternator
    By JeremyBrown87 in forum NETA Level 3 Exam
    Last Post: March 29, 2019, 11:57 AM
Tags for this Thread
Related Content
Follow us
Explore TestGuy
NETA Certification Training
NICET Electrical Power Testing
Help and Support