Results 1 to 8 of 8
What is the closest distance for an unqualified worker?
  1. test11's Avatar
    test11 is offline
    There can be only one!
    Member
    Mar 2017
    A hotel near you
    38
    In the picture below, what is the closest distance for an unqualified worker when the equipment is open?
    It should be 42" because he can wear PPE and be in the boundary. If he needs to be closer, than 42", he can get within 12" with an escort.
    Apr 2020
    Quote Originally Posted by test11 View Post
    3. Restricted approach boundary
    The restricted approach boundary is the distance from an exposed part which is considered the same as making contact with the live part. Only qualified personnel wearing appropriate personal protective equipment (PPE), having specified training to work on energized conductors or components, and a documented plan justifying the need to perform this work may cross the boundary and enter the Restricted Space. Insulated gloves, tools, and equipment are required within this boundary.
    it sounds like you answered your own question. 42" without supervision but not qualified so can't go within 12. I would say the answer is 12"
    Apr 2020
    Quote Originally Posted by demtxboyz View Post
    well I just took a test and its not 12"
  7. test11's Avatar
    test11 is offline
    Member
    Mar 2017
    A hotel near you
    38
    I posted this and other questions in the problem report thread originally. I guess they want to discuss before any changes.
    Dec 2021
    1"-12" is your prohibited approach boundary
    12"-42" is your restricted approach boundary
    42"-48" is your limited approach boundary
    48"+ is your flash protection boundary
    Only qualified personnel can go in the restricted approach boundary, so unqualified personnel are limited to The limited approach boundary with supervision. Therefore wouldn't the answer be 42"?
    Nov 2021
    8
    You can’t wear PPE effectively without being trained on it.
    From Fluke:
    Arc flash boundary
    The arc flash boundary, or restricted approach boundary, changes depending on the potential arc flash hazard. The arc flash boundary is calculated to 1.2 calories/cm2 of incident energy. That’s the distance where a worker without appropriate PPE would receive second-degree burns.
    Sometimes this boundary is the furthest one from the exposed equipment, other times the limited approach boundary is the furthest out. When the arc flash boundary is the furthest away, it becomes the line no one should pass without training and PPE. If the limited approach boundary is further out, then that should be treated as the line no one should pass without training and PPE.
  13. Robert0 is offline Junior Member Pro Subscriber
    Aug 2021
    in the practice test it is 12
    Jun 2022
    34
    Answer is 12" in the practise test
  1. Arc flash incident energy reduction over distance
    By mbaxter1 in forum NETA Level 2 Exam
    Last Post: February 18, 2020, 09:01 AM
  2. Fall-of-potential C2 distance
    By marvinray in forum Electrical Testing Talk
    Last Post: August 9, 2018, 03:20 PM
  3. Electrician performs CPR after worker is shocked by outdoor transformer
    By testguy in forum Safety and Arc Flash Talk
    Last Post: June 27, 2018, 12:59 PM
  4. Maintenance worker survives sustained electrical shock
    Last Post: March 14, 2016, 06:45 PM
