    Neutral testing on breaker

    How do you guys Primary injection the neutral of a 4 pole breaker? It has a setting which I知 guessing is for over current on the return?

  2. #2
  3. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    374
    Reputation
    Quote Originally Posted by TrapFlyVenus View Post
    How do you guys Primary injection the neutral of a 4 pole breaker? It has a setting which I知 guessing is for over current on the return?
    Test just like any other pole, I've run into a lot of these on Square D Masterpacts in data center UPS systems.

  4. #3
  5. nolanholt is offline Junior Member Pro Subscriber
    Join Date
    Mar 2019
    Posts
    3
    Reputation
    Quote Originally Posted by TrapFlyVenus View Post
    How do you guys Primary injection the neutral of a 4 pole breaker? It has a setting which I知 guessing is for over current on the return?
    Test just like the other phases. Sometimes the neutral pole doesn't have overcurrent protection so don't be surprised if you try to test it and it doesn't trip. Is it a molded case or insulated case?

  6. #4
  7. Join Date
    Jun 2017
    Posts
    16
    Reputation
    Quote Originally Posted by TrapFlyVenus View Post
    How do you guys Primary injection the neutral of a 4 pole breaker? It has a setting which I知 guessing is for over current on the return?
    The neutral pole you test like any other pole like has been said before. You have to realize that all neutral poles are different on different breakers.

    Some neutral poles have no protection and are just a switch for that pole, some have settings that will trip at half or full value of the trip settings. Others only have some trip settings, like the large Magnum DS with 8 poles, on those there are 2 neutral poles and the only trip fiction on the neutral is ground fault and maintenance mode.

Subscribe

Login or register to leave a reply!


Share this thread

Related Topics

  1. How to Size Transformer Neutral Resistor
    By AlexT90 in forum NETA Level 3 Exam
    Replies: 4
    Last Post: November 7, 2019, 09:52 AM
  2. Free courses on the basics of breaker testing
    By tylerfini3 in forum Electrical Testing Talk
    Replies: 3
    Last Post: October 17, 2019, 05:13 PM
  3. Transformer neutral connection
    By sahoojoge in forum Electrical Testing Talk
    Replies: 4
    Last Post: July 18, 2019, 08:57 AM
  4. Circuit Breaker Grounding Cart Testing
    By roberts311 in forum Electrical Testing Talk
    Replies: 2
    Last Post: May 16, 2018, 02:06 AM
  5. Neutral CT testing
    By bwillsey88 in forum Electrical Testing Talk
    Replies: 2
    Last Post: May 18, 2017, 10:32 AM


Related Content


Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support