    How do you guys Primary injection the neutral of a 4 pole breaker? It has a setting which I知 guessing is for over current on the return?
    411
    Quote Originally Posted by TrapFlyVenus View Post
    Test just like any other pole, I've run into a lot of these on Square D Masterpacts in data center UPS systems.
    Mar 2019
    Test just like the other phases. Sometimes the neutral pole doesn't have overcurrent protection so don't be surprised if you try to test it and it doesn't trip. Is it a molded case or insulated case?
    Jun 2017
    25
    The neutral pole you test like any other pole like has been said before. You have to realize that all neutral poles are different on different breakers.
    Some neutral poles have no protection and are just a switch for that pole, some have settings that will trip at half or full value of the trip settings. Others only have some trip settings, like the large Magnum DS with 8 poles, on those there are 2 neutral poles and the only trip fiction on the neutral is ground fault and maintenance mode.
  1. Free courses on the basics of breaker testing?
    By tylerfini3 in forum Electrical Testing Talk
    Last Post: February 2, 2020, 11:47 AM
  2. How to Size Transformer Neutral Resistor
    By AlexT90 in forum NETA Level 3 Exam
    Last Post: November 7, 2019, 09:52 AM
  3. Transformer neutral connection
    By sahoojoge in forum Electrical Testing Talk
    Last Post: July 18, 2019, 08:57 AM
  4. Circuit Breaker Grounding Cart Testing
    By roberts311 in forum Electrical Testing Talk
    Last Post: May 16, 2018, 02:06 AM
  5. Neutral CT testing
    By bwillsey88 in forum Electrical Testing Talk
    Last Post: May 18, 2017, 10:32 AM