    Tan Delta versus Partial Discharge testing on cables

    Thoughts on this? What is the preferred test for all of you, and why?






    www.taifaengineering.com

  2. #2
  3. Join Date
    Jun 2017
    Posts
    16
    Reputation
    Quote Originally Posted by TaifaEngineering View Post
    Thoughts on this? What is the preferred test for all of you, and why?






    www.taifaengineering.com
    It all depends on the application. In general I feel that the Tan Delta is the better test but it is more invasive the cable must be de-energized and made safe. The Partial Discharge testing if they have the hardware installed can be done live.

    In general for a site that has infrequent shutdowns Partial Discharge would be the way to go and it can provide information on problem cables that you can then check with Tan Delta during a shutdown.

  4. #3
  5. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member Pro Subscriber
    Join Date
    Feb 2018
    Location
    Richmond, VA
    Posts
    127
    Reputation
    Quote Originally Posted by Nick1234 View Post
    It all depends on the application. In general I feel that the Tan Delta is the better test but it is more invasive the cable must be de-energized and made safe. The Partial Discharge testing if they have the hardware installed can be done live.

    In general for a site that has infrequent shutdowns Partial Discharge would be the way to go and it can provide information on problem cables that you can then check with Tan Delta during a shutdown.
    My last company recommended performing Online PD annually, and every 5 years performing Tan-Delta or Offline Partial Discharge since OLPD doesn't detect minor electrical treeing, while the offline test can.

    I believe the overall difference lies in the cost and safety placed on the customer to work around. Tan-delta is cheaper (I have determined failure in a cable within 3 months with TD), but Offline Partial Discharge is much more accurate, and Online Partial Discharge is more convenient to continued operations.

  6. #4
  7. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    374
    Reputation
    Quote Originally Posted by TaifaEngineering View Post
    Thoughts on this? What is the preferred test for all of you, and why?
    www.taifaengineering.com
    Offline PD is the most accurate if you are going to take the cable down but is really specialized and expensive. Tan Delta combined with VLF will give you a good baseline for comparison in the future and is much cheaper. Online PD is a good non-distructive test, but like an infrared scan its only useful for monitoring, not a replacement for offline maintenance.

    From NETA World Spring 2017: Tan delta tests the health of the insulation as an average value of the length of the cable, and therefore, small sections with significant defects cannot be detected. Partial discharge detects these small defects but cannot detect aging effects (like water trees) until they result in discharge. Thus, these two tests are complementary, and it is advisable to do both at the commissioning of any cable.

    https://www.eatechnology.com/america...17_FlowONE.pdf

Subscribe

Login or register to leave a reply!


Share this thread

Related Topics

  1. Minimum discharge time
    By Cldpmu in forum NETA Level 2 Exam
    Replies: 3
    Last Post: December 21, 2018, 10:08 PM
  2. Tan / Delta or Power Factor Testing of Dry Type Transformer
    By mask12900 in forum Electrical Testing Talk
    Replies: 1
    Last Post: January 1, 2018, 08:41 PM
  3. Safely discharge HV feeder using load break disconnect switch (procedure)
    By SecondGen in forum Safety and Arc Flash Talk
    Replies: 2
    Last Post: December 13, 2017, 06:50 PM
  4. Partial Discharge Data Interpretation
    By ies0900012 in forum Electrical Testing Talk
    Replies: 2
    Last Post: July 21, 2016, 06:27 PM
  5. How much spacing should you have when testing cables?
    By cjones09 in forum Safety and Arc Flash Talk
    Replies: 5
    Last Post: September 21, 2015, 02:52 PM


Related Content


Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support