    Given a circuit breaker schematic what happens after the 51 element trips?
    A) Trip coil energizes and opens the breaker
    B) 86-1 contacts close
    C) 86-1 and 86-2 relay operates
    D) 86-1 relay operates
    E) 86-2 relay operates
    its hard to read this diagram can anyone help?
    Click image for larger version.
  2. #2
  3. Warrengarber's Avatar
    Warrengarber is offline
    If you ignore it, it will fail.
    Seasoned Member
    Join Date
    Jul 2017
    Location
    Jacksonville, FL
    Posts
    58
    Reputation
    It is really hard to see but the two 50/51 elements in the SR relay operate and next will operate the 86-1 and the 86-2 lock out relays. The two lock out relays will then energize the trip coil (TC). So I think the answer should be C.
    Quote Originally Posted by mbaxter1 View Post
    Warren Garber
    Have a great day!
  4. #3
  5. Join Date
    Jun 2017
    Posts
    25
    Reputation
    Quote Originally Posted by Warrengarber View Post
    This is what i see too, though there are some NO and NC contacts before and after the 86-1 and the 86-2 lock out relays which are not labeled. Depending on which state they are in could change the answer
  6. #4
  7. GreenHornet's Avatar
    GreenHornet is offline
    Riddle me this Batman
    Junior Member
    Join Date
    Jun 2018
    Location
    Vermont
    Posts
    13
    Reputation
    looks like there is 2 51 relays so like which ever one operates trips the associated 86/lockout which trips the breaker
  8. #5
  9. GreenHornet's Avatar
    Junior Member
    Join Date
    Jun 2018
    Location
    Vermont
    Posts
    13
    Reputation
    looks like 2 51 relays, each trip their own 86/lockout which trips the breaker
  10. #6
  11. Join Date
    Dec 2017
    Posts
    30
    Reputation
    A)Trip coil energizes and opens the breaker
    B and D are correct! Relay 86-1 will operate due to the closed contact and will energize TC.
    C and E are wrong. Relay 86-2 will never operate due to the open contact.
  12. #7
  13. keatigp is offline Junior Member Pro Subscriber
    Join Date
    Mar 2021
    Posts
    1
    Reputation
    Quote Originally Posted by Nick1234 View Post
    The normally closed contacts surrounding a lockout coil in most cases are contacts that open on the operation of a lockout to protect its own coil.
Subscribe
Login or register to leave a reply!
Share this thread
Related Topics
  1. Ground fault trips at half of setting
    By joenavymctest in forum P&C / Relay Testing Talk
    Last Post: March 6, 2020, 08:45 AM
Tags for this Thread
Related Content
Follow us
Explore TestGuy
NETA Certification Training
NICET Electrical Power Testing
Help and Support