Not a test question - Transformer ester oil question

    #1
  1. Join Date
    Aug 2018
    Posts
    4
    Reputation

    Not a test question - Transformer ester oil question

    I'm looking at a transformer assembly job, the transformer is from Siemens and is insulated with Ester oil. I've only worked with Mineral oil before, are there any differences in the way we should handle the Ester oil?

    My initial thoughts would be new pump and hoses so as not to contaminate with the mineral oil residue in our existing equipment.

    I've read that the ester oil is not affected by moisture/water ingress, does that mean a nitrogen blanket is not required? I feel like Nitrogen or dry air still makes sense but just wanting to clarify if any one has some experience with this product.

    Thanks

  2. #2
  3. Join Date
    Feb 2018
    Location
    Richmond, VA
    Posts
    113
    Reputation
    Quote Originally Posted by JamesM View Post
    I'm looking at a transformer assembly job, the transformer is from Siemens and is insulated with Ester oil. I've only worked with Mineral oil before, are there any differences in the way we should handle the Ester oil?

    My initial thoughts would be new pump and hoses so as not to contaminate with the mineral oil residue in our existing equipment.

    I've read that the ester oil is not affected by moisture/water ingress, does that mean a nitrogen blanket is not required? I feel like Nitrogen or dry air still makes sense but just wanting to clarify if any one has some experience with this product.

    Thanks
    First question would be is it Synthetic or Natural Ester Fluid?

    https://www.midel.com/blog/about-esters/

    Synthetic esters are manufactured from carefully selected raw materials to give a finished product that is tailored to the specific application. In the case of MIDEL 7131 it has been developed specifically to be used as a transformer dielectric; hence it is a high performance fluid which is suitable for use in all types of application. Crucially, MIDEL 7131 has a very low pour point and excellent oxidation stability, making it suitable for cold climates and breathing systems where the fluid is exposed to oxygen from the air.

    Natural esters are made from renewable natural sources, for example MIDEL eN 1204 (rapeseed/canola) and MIDEL eN 1215 (soybean). The base oil is chosen to give the best possible fit to the application; however unlike synthetic esters the properties of these base oils cannot be significantly altered. Therefore in order to get a natural ester dielectric fluid that remains liquid at low temperatures a compromise has to be made, and a base oil with reduced oxidation stability is usually chosen. This means that natural esters are only suitable for sealed equipment. Natural esters also have high pour points when compared to synthetic esters, and so are best suited to temperate locations or indoor applications.

    FR3 would also be a form of Natural Esters.

    https://www.cargill.com/bioindustrial/envirotemp/fr3

  4. #3
  5. Join Date
    Nov 2019
    Posts
    7
    Reputation
    Quote Originally Posted by JamesM View Post
    I'm looking at a transformer assembly job, the transformer is from Siemens and is insulated with Ester oil. I've only worked with Mineral oil before, are there any differences in the way we should handle the Ester oil?

    My initial thoughts would be new pump and hoses so as not to contaminate with the mineral oil residue in our existing equipment.

    I've read that the ester oil is not affected by moisture/water ingress, does that mean a nitrogen blanket is not required? I feel like Nitrogen or dry air still makes sense but just wanting to clarify if any one has some experience with this product.

    Thanks
    i like to use new hoses when working with different oil. i would put a nitrogen blanket for good practice.

Subscribe

Login or register to leave a reply!


Share this thread

Related Topics

  1. XFMR test question - wye-delta TTR
    By dbryce89 in forum NETA Level 2 Exam
    Replies: 16
    Last Post: March 13, 2019, 06:56 PM
  2. Practice Test Question: Interfacial Tension
    By EricGoetz92 in forum NETA Level 3 Exam
    Replies: 4
    Last Post: January 4, 2019, 11:33 AM
  3. Insulation resistance test set question
    By mkennedyShermco in forum NETA Level 4 Exam
    Replies: 2
    Last Post: June 10, 2018, 12:52 PM
  4. Test Question--High Current Injection
    By alexlounsbury in forum NETA Level 3 Exam
    Replies: 5
    Last Post: July 10, 2017, 11:38 AM
  5. Replies: 4
    Last Post: January 24, 2015, 01:34 PM

Tags for this Thread



Related Content


Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support