Page 2 of 2 FirstFirst 12
Results 11 to 13 of 13
How do you Defeat Ground Fault with Primary Injection on Eaton 310+? Trip Unit
    Mar 2015
    33
    Quote Originally Posted by Warrengarber View Post
    How did it go?
    Nothing worked for me with this secondary test set. Had to go "in and out" to defeat the ground fault on the trip units. Thankfully I dont see these breakers that often. There was a few Eaton reps on the job as well and they didnt even have an answer for me. Not a fan of these breakers
    Jul 2020
    How should I remove the dummy connector??
    Hello!
    I just got a secondary injection test kit for a digitrip 310+ and I just can't take out this dummy connector to make it a male one... it seems to be impossible.. it is like a one-piece plastic connector...
    Any of you have done it before?
    Thank you in advance
    It says on page 7 of the Instruction Leaflet IL5721B13H07 for the secondary test kit that you must first turn off the ground fault function before secondary testing so I would assume that there is a ground fault defeat switch. That is the test set that has a different card for each trip unit with a dial and a push button. If I remember correctly there is a module that you plug in line that has a button that defeats ground fault. Below is from page 7. Hope this helps.
    "Digitrip 310+
    Digitrip 310+ Circuit Breakers Test Procedure
    Setup
    Before testing, write down all settings in use so that they may be
    restored after tests are completed.
    To begin testing;
    1. Connect the Digitrip 310+ cable assembly (style 5721B14) into
    the side connector of the handheld unit. Plug the other end of
    the cable into the test port.
    Note: The test plug may be covered by a “dummy connector” used to
    protect the test plug pins during shipment. Ease the dummy connector
    off using a screw driver to expose the male test pins underneath.
    2. Position Trip/No Trip switch on cable assembly to the Trip position
    and set the Ground Fault switch to the “Off” position."
    168
    Quote Originally Posted by cmferrer View Post
    Hello!
    I usually just take a pair of needle nose pliers and pull the black cover (dummy connector) straight out with no issues. If your having issues, you might have a bent pin inside.
  1. Primary Current Injection instantenous Pickup
    Last Post: May 3, 2020, 02:43 PM
  2. Easy method for ground fault testing EATON 310 and 310+ trip units
    Last Post: October 31, 2018, 04:52 PM
  3. Primary Current Injection Test
  4. Primary current injection 138kV breaker with bushing CT's
  5. Replies: 1
    Last Post: March 2, 2016, 04:59 PM