    MVT Plus to AC Pro Settings

    I have several breakers I need to convert settings from MVT and MVT Plus to AC Pro. Is there a conversion chart out there on the free market? We send the settings requests to our engineering staff, but it seems like this should be accomplished at technician level in case of emergencies. Thank you in advance for your suggestions.

  2. #2
  3. Join Date
    Sep 2017
    Posts
    8
    Reputation
    My company does AC PRO trip unit retrofits quite often and I perform the final testing on them. I probably test 3 or 4 a month.
    To my knowledge, there are not any conversion charts and the only way to accurately program the same tripping values into the AC PRO would be consulting the time current curves of both trip units, and trying to match the pickup and delay values to the best of your abilities.
    When our end users have AC Pro trip units installed, they always consult engineering staff and reference the local distribution studies to obtain trip unit settings prior to placing it in service, and we ship the circuit breakers with all minimum trip values so they can be set by customer.

  4. #3
  5. Join Date
    Sep 2017
    Posts
    8
    Reputation
    Also, the AC Pro team are always very helpful and easy to establish a good working relationship with. I would encourage you to give them a call and see if they can help you out. They are always more than happy to help me out with any requests that I have.
    Good Luck!

  6. #4
  7. Join Date
    Sep 2019
    Location
    MI
    Posts
    4
    Reputation
    Quote Originally Posted by AaronCBI View Post
    Also, the AC Pro team are always very helpful and easy to establish a good working relationship with. I would encourage you to give them a call and see if they can help you out. They are always more than happy to help me out with any requests that I have.
    Good Luck!
    I plan to call them in the morning. Unfortunately, that doesn’t help me tonight. Thank you for the reply.

  8. #5
  9. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    358
    Reputation
    Quote Originally Posted by bbryant View Post
    I plan to call them in the morning. Unfortunately, that doesn’t help me tonight. Thank you for the reply.
    If you need an answer right away I would suggest comparing the Time Current Curves of the two trip units. Look up the time tolerance for each MVT setting and compare to the tables and curves in the AC Pro manual. You can find all the necessary documents online.

  10. #6
  11. Join Date
    Feb 2018
    Location
    Richmond, VA
    Posts
    107
    Reputation
    Quote Originally Posted by bbryant View Post
    I have several breakers I need to convert settings from MVT and MVT Plus to AC Pro. Is there a conversion chart out there on the free market? We send the settings requests to our engineering staff, but it seems like this should be accomplished at technician level in case of emergencies. Thank you in advance for your suggestions.
    I agree with SecondGen above, in a hurry, you have to match the AC Pro trip curves as close to the replaced trip unit trip curves. I disagree that this should be accomplished at the technician level since it requires a PE to determine the settings and absorb the liability and responsibility of the arc flash hazard created from the SCCS. As a technician, I don't want to be the one going to court after an incident occurs based on the settings inputted into the breaker without proper coordination, god forbid it results in injury or death.

    I always remind the customer that the settings are only a close representation of the original study, and that in accordance with NFPA 70E, a revision of the Arc Flash study and SCCS need to be updated as the electrical distribution system has been altered and now violates the NFPA 70E Arc Flash Risk Assesment, which also will require engineering to determine the proper settings for the altered breakers.

    NFPA 70E 130.5(G)
    The incident energy analysis shall be updated when changes
    occur in the electrical distribution system that could affect the
    results of the analysis. The incident energy analysis shall also be
    reviewed for accuracy at intervals not to exceed 5 years.

Subscribe

Login or register to leave a reply!


Share this thread

Related Topics

  1. Generic Trip Settings for Circuit Breakers?
    By SecondGen in forum P&C / Relay Testing Talk
    Replies: 1
    Last Post: May 9, 2018, 08:12 PM


Related Content


Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support