Determine total reactive resistance of this circuit
    Mar 2018
    18
    This question appeared on the NETA III exam.
    Find the total reactance in this circuit. I distinctly remember it because it was the very first question to hit me and I said "Gee thanks alot".
    I wasn't quite ready for it.
Name:	NETA Schematic.jpg
  3. rofo42 is offline Member Pro Subscriber
    29
    Quote Originally Posted by whiskers View Post
    I'll take a stab at this...
    Capacitors in series are found using the reciprocal or product over sum method. This gives a total of 10 uF. (20*20 = 400. 400/40=10)
    Capacitors in parallel are added together. 10 uF + 25 uF = 35 uF
    Capacitive Reactance (Xc) = 1 / 2*pie*F*C ( 2 * 3.14 * 60 * .000035 = .013188) 1/.013188 = 75.82
    Xc = 76
    Inductors in parallel are found using the reciprocal or product over sum method. 1/250 + 1/250 = .008 (1/.008 = 125 mH
    Inductors in series are added together. 500 mH + 125 mH = 625 mH
    Inductive Reactance = 2*pie*F*H (2*3.14*60*.625 = 235.5)
    Xl = 236
    Xc + Xl (76 + 236) = 312 ohms
    I would be surprised if I did that correctly. Someone correct me if needed!
    Sep 2015
    I think you're correct up to this point.
    Looking at the equation sheet, it should be XL - XC
    So doing that I get 160 ohms.
    I'd be willing to bet that both 160 and 312 are possible answers on the test.
  7. Warrengarber's Avatar
    Warrengarber is offline
    Seasoned Member Pro Subscriber
    Jul 2017
    Jacksonville, FL
    57
    Your math all works out to me. A time saver when performing this and from my experience with similar questions on the test is that they will use two identical, in this case capacitors in series and reactors in parallel, values. When this is the case the calculated value is half of one of the identical capacitors.
    Capacitor Example: Look at Rofo42's capacitors 20ufx20uf=400uf over the sum of 20uf+20uf= 40uf, 400uf/40uf=10uf or half of one of the 20uf capacitors. (Capacitors in series)
    Inductor Example: 1/250mH+1/250mH=0.004mH+0.004mH=0.008mH then 1/0.008 with a result of 125mH or half of one of the two parallel 250mH reactors (Reactors in Parallel)
    It is all about the time it takes to answer the questions on the test. Remembering these shortcuts during the stress of taking the test and knowing that that one wrong answer may be the make or break is not easy. A question like this could take 5 minutes to answer when doing all of the math but when you only have an average of 72 seconds to answer a question shortcuts count. I hope that helps and great job Rofo42
    Xc = 76
    Xl = 236
    Warren Garber
    Have a great day!
    Mar 2018
    18
    Yes the math does work out.
    However as stated, two inductors in parallel of equal value = 1/2 the inductance of both and 2 capacitors in series of equal value, likewise = 1/2 the capacitance of both. No need for the math.
    Whiskers
  11. Kalbi_Rob's Avatar
    Richmond, VA
    138
    Xc = 76
    Xl = 236
    I disagree with the above post, the math is almost good. Only problem I see is you cannot just add Capacitive Impedance and Inductive Impedance together, remember the phase angles are up to 180 degrees apart.
    ZT2=XR2+(|XL-XC|)2
    So, since there is no XR
    ZT=(236-76)=160 Ohms
  13. Warrengarber's Avatar
    Jul 2017
    Jacksonville, FL
    57
    Thank you for the catch. I see on the formula sheet that they have the formula for Z and you are very correct.
    Z= the square root of R squared plus (XL-Xc) squared
    ZT2=XR2+(|XL-XC|)2
    Warren Garber
    Have a great day!
  15. rofo42 is offline Member Pro Subscriber
    29
    ZT2=XR2+(|XL-XC|)2
    I did not know this. Thank you for the information!
    Mar 2018
    18
    Well, that throws a wrench in the works but, the question was not looking for the impedance of the circuit but simply the reactive component of the circuit at 60 hz.
    While the math is correct about the phase angles, I'm not sure what the exact wording of the question was or what 4 choices were available, wish I knew.
  19. Kalbi_Rob's Avatar
    Richmond, VA
    138
    Impedance must be calculated for each component (i.e. the capacitive impedance, inductive impedance and resistive impedance) to calculate the total reactance of the circuit. Without the frequency, you cannot determine the reactance of the circuit as inductors and capacitors react differently at different frequencies.
    This page explains it alot better than I do:
    https://www.wikihow.com/Calculate-Impedance
  1. Determine the approximate short circuit current available
    By rasilva in forum NETA Level 3 Exam
    Last Post: December 21, 2018, 06:25 PM
  2. Reactive Power (KVAR)
    Last Post: December 26, 2017, 03:09 AM
  3. What is the reactive power?
    Last Post: October 5, 2017, 03:33 PM
  4. Total XC for capacitors in parallel
    By adamr8223 in forum NETA Level 3 Exam
    Last Post: December 4, 2016, 02:08 AM
  5. Total burden on current transformer
    By Sanjayo in forum NETA Level 3 Exam
    Last Post: February 19, 2016, 01:50 PM