    Electrical Single Line Question

    Hello All,

    When looking at a single line drawing, if circuit breaker ratings don't specify AT or AF but only have one rating, such as 400A, does that indicate the breaker is a 400AF or set to 400AT?

    I hope my question makes sense.

    Thanks!

  2. #2
  3. Join Date
    Apr 2018
    Location
    Michigan
    Posts
    40
    Reputation
    Quote Originally Posted by Joshua122042 View Post
    Hello All,

    When looking at a single line drawing, if circuit breaker ratings don't specify AT or AF but only have one rating, such as 400A, does that indicate the breaker is a 400AF or set to 400AT?

    I hope my question makes sense.

    Thanks!
    It is likely a designation for a fixed size breaker, where there is no ability to vary the breaker rating via a rating plug or settings. It could also be preliminary design drawings were the type/manufacturer of the breakers is not known, so it is simply specifying the required rating, which in this example could end up being something like 800AF/400AT or several other legitimate combinations.

  4. #3
  5. Join Date
    Sep 2018
    Posts
    2
    Reputation
    Quote Originally Posted by Wanderer20001us View Post
    It is likely a designation for a fixed size breaker, where there is no ability to vary the breaker rating via a rating plug or settings. It could also be preliminary design drawings were the type/manufacturer of the breakers is not known, so it is simply specifying the required rating, which in this example could end up being something like 800AF/400AT or several other legitimate combinations.
    Thanks for the info! This answer my questions perfectly.

  6. #4
  7. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    343
    Reputation
    Quote Originally Posted by Joshua122042 View Post
    Hello All,

    When looking at a single line drawing, if circuit breaker ratings don't specify AT or AF but only have one rating, such as 400A, does that indicate the breaker is a 400AF or set to 400AT?

    I hope my question makes sense.

    Thanks!
    Most likely the frame provision for that section. Switchgear cells are typically sized for a specific frame size and the sensors/plug are used to determine the continuous current rating for the particular load.