    Quote Originally Posted by Kalbi_Rob View Post
    You just put all the resistances in parallel between the end 15 ohm resistances. They are in series on the parallel bus bars.

    R= 15+(1/((1/(5+10+5)+(1/(5+10+5)))+15 = 15+(1/((1/20)+(1/20)))+15 = 15+10+15 = 40

    Don't quote me on this being the right answer, but that's how I see it.
    That is how I see it also. This question was also on my level II test.

    This is how I visualize it.
    Click image for larger version. 

Name:	Total-resistance.jpg 
Views:	11 
Size:	60.0 KB 
ID:	417

  2. #12
  3. Join Date
    Mar 2015
    Posts
    10
    Reputation
    Quote Originally Posted by rofo42 View Post
    That is how I see it also. This question was also on my level II test.

    This is how I visualize it.
    Click image for larger version. 

Name:	Total-resistance.jpg 
Views:	11 
Size:	60.0 KB 
ID:	417
    Thank you

  4. #13
  5. clipboardwarrior's Avatar
    clipboardwarrior is offline Junior Member Pro Subscriber
    Join Date
    Mar 2018
    Posts
    13
    Reputation
    Quote Originally Posted by SecondGen View Post
    Easy way to calculate:
    A2 + B2 = C2

    750,000 = C2
    750,000 x 0.95 = 712,500 = A2
    750,000 - 712,500 = 37,500 = B2
    sqrt(37,500) = 193.64
    I agree with most of this. Until you came up with B2.

    sqrt(750,000sq - 712,500sq) = 234.42 = B2

    Thoughts? I know this is an old post, but, for those of us studying, it's still relevant.

  6. #14
  7. jgraves is offline Junior Member Pro Subscriber
    Join Date
    Jan 2018
    Posts
    6
    Reputation
    Quote Originally Posted by clipboardwarrior View Post
    I agree with most of this. Until you came up with B2.

    sqrt(750,000sq - 712,500sq) = 234.42 = B2

    Thoughts? I know this is an old post, but, for those of us studying, it's still relevant.
    I don't think A^2+B^=C^2 method is the right way to go about the problem. Kw loading will stay the same, but changing the kvar will cause the kva to change.

    Page 4 of (https://www.eaton.com/ecm/groups/pub...a02607001e.pdf) has a good visual of the change.

    The OP's method seems the quickest to answer the problem:
    1. Solve for kw. (pf x KVAinitial =kw) --- 0.75 x 750000 = 562500 Kw
    2. Find the angle for .95 pf. (cos-1 [Pfdesired]= angle) --- cos-1 (0.95) = 18.19 degrees
    3. Solve for Kvar. (tan[angle] x kw = kvar) --- tan(18.19) x 562500 = 184831 Kvar


    For fun you can then use A^2+B^=C^2 to solve for the new Kvar = 592088 Kvar

  8. #15
  9. clipboardwarrior's Avatar
    clipboardwarrior is offline Junior Member Pro Subscriber
    Join Date
    Mar 2018
    Posts
    13
    Reputation
    Quote Originally Posted by jgraves View Post
    I don't think A^2+B^=C^2 method is the right way to go about the problem. Kw loading will stay the same, but changing the kvar will cause the kva to change.

    Page 4 of (https://www.eaton.com/ecm/groups/pub...a02607001e.pdf) has a good visual of the change.

    The OP's method seems the quickest to answer the problem:
    1. Solve for kw. (pf x KVAinitial =kw) --- 0.75 x 750000 = 562500 Kw
    2. Find the angle for .95 pf. (cos-1 [Pfdesired]= angle) --- cos-1 (0.95) = 18.19 degrees
    3. Solve for Kvar. (tan[angle] x kw = kvar) --- tan(18.19) x 562500 = 184831 Kvar


    For fun you can then use A^2+B^=C^2 to solve for the new Kvar = 592088 Kvar
    You're absolutely right. Between the time I read the OP and then read the follow up comment, I spaced on the VA changing! Yoinks! Hopefully, I don't pull any dumb stunts like that next week when I take my test.

Page 2 of 2 FirstFirst 12
Subscribe

Login or register to leave a reply!


Share this thread

Related Topics

  1. Practice Exam Upgrades Summer 2019
    By testguy in forum News and Announcements
    Replies: 3
    Last Post: July 17, 2019, 04:16 PM
  2. NETA III TEST Jan 2019
    By cbrazzil in forum NETA Level 3 Exam
    Replies: 1
    Last Post: April 19, 2019, 11:59 AM
  3. Who Else is Taking Level 4 in January 2019?
    By Wanderer20001us in forum NETA Level 4 Exam
    Replies: 0
    Last Post: December 26, 2018, 12:51 PM

Tags for this Thread



Related Content


Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support