    In an open delta with single-phase loads, the high leg must be identified by orange

    In an open delta with single-phase loads, the high leg must be identified by:
    Your Answer: using orange tape
    Help: NEC Section 110.15

    This was marked incorrect, but I do not understand how this is wrong after reviewing the NEC Section 110.15 It tells you to mark the high leg as orange.

  2. #2
  3. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member
    Join Date
    Feb 2018
    Location
    Richmond, VA
    Posts
    114
    Reputation
    Quote Originally Posted by Spanky123 View Post
    In an open delta with single-phase loads, the high leg must be identified by:
    Your Answer: using orange tape
    Help: NEC Section 110.15

    This was marked incorrect, but I do not understand how this is wrong after reviewing the NEC Section 110.15 It tells you to mark the high leg as orange.
    After reading NEC 110.15, it seems like the question is not accurate, as it talks about a 4 wire Delta system in which one winding is grounded in the middle and a neutral is landed at that point. This would not be an open delta system as Open delta is a 3 wire system with B phase grounded.

  4. #3
  5. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    364
    Reputation
    Quote Originally Posted by Kalbi_Rob View Post
    After reading NEC 110.15, it seems like the question is not accurate, as it talks about a 4 wire Delta system in which one winding is grounded in the middle and a neutral is landed at that point. This would not be an open delta system as Open delta is a 3 wire system with B phase grounded.
    Agree that this question should read 4-wire Delta system rather than open delta. As for the orange marking, 2015 edition states "orange in color or by other effective means."

    Not sure what the other options are but "other effective means" implies that markings other than orange are still acceptable. Pic related.

    Click image for larger version. 

Name:	nec-110-15-high-leg-marking-excerpt.jpg 
Views:	1 
Size:	142.5 KB 
ID:	378

Subscribe

Login or register to leave a reply!


Share this thread

Related Topics

  1. Electrical Single Line Question
    By Joshua122042 in forum Electrical Testing Talk
    Replies: 3
    Last Post: June 27, 2019, 09:36 AM
  2. Open Delta Calculation
    By Kalbi_Rob in forum NETA Level 3 Exam
    Replies: 1
    Last Post: August 29, 2018, 01:32 PM
  3. Protection and Control / Relay Testing Forum Now Open
    By testguy in forum News and Announcements
    Replies: 0
    Last Post: July 6, 2018, 02:13 PM
  4. NICET Forum Now Open
    By testguy in forum News and Announcements
    Replies: 0
    Last Post: July 6, 2018, 01:10 PM

Tags for this Thread



Related Content


Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support