    Percentage differential relay - What is the calculated imbalance?

    A percentage differential relay with a 25 percent slope characteristic has 4.9 A in one restraint coil and 4.2A in the other. What is the calculated imbalance?

    I have the answer from the help link of 16.6% but need help on the formulas used and calculation process.

  2. #2
  3. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member
    Join Date
    Feb 2018
    Location
    Richmond, VA
    Posts
    108
    Reputation
    Quote Originally Posted by jbren81 View Post
    A percentage differential relay with a 25 percent slope characteristic has 4.9 A in one restraint coil and 4.2A in the other. What is the calculated imbalance?

    I have the answer from the help link of 16.6% but need help on the formulas used and calculation process.
    First determine the difference between the restraint coils:
    4.9A - 4.2A = 0.7A

    Then calculate the % slope by using the smaller restraint coil current (can use either but the higher % slope is from the smaller restraint current):
    0.7A / 4.2A = 0.166 * 100% = 16.6%.

    16.6% < 25% so the relay will not operate.

  4. #3
  5. jbren81 is offline Junior Member Pro Subscriber
    Join Date
    Mar 2019
    Posts
    2
    Reputation
    Quote Originally Posted by Kalbi_Rob View Post
    First determine the difference between the restraint coils:
    4.9A - 4.2A = 0.7A

    Then calculate the % slope by using the smaller restraint coil current (can use either but the higher % slope is from the smaller restraint current):
    0.7A / 4.2A = 0.166 * 100% = 16.6%.

    16.6% < 25% so the relay will not operate.
    Thank you, I appreciate the help!

Subscribe

Login or register to leave a reply!


Share this thread

Related Topics

  1. Field test procedure for Modified Differential Ground Fault systems
    By Biscuit in forum Electrical Testing Talk
    Replies: 3
    Last Post: January 13, 2016, 01:39 AM


Related Content


Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support