    NETA III TEST Jan 2019

    NETA III TEST -
    Items on the last test pooled from several techs

    1. What does a bell alarm do?

    2. In the diagram where is the anti pump relay located?
    Click image for larger version. 

Name:	anit pump.png 
Views:	93 
Size:	20.4 KB 
ID:	337

    3. What is this device?
    Click image for larger version. 

Name:	network.png 
Views:	14 
Size:	1.04 MB 
ID:	338
    A) Network protector
    B) mining breaker
    C) chemical unit breaker
    D) Metal enclosed breaker

    4. On a 87 diff relay, the tap screw was found to be loose but tripped. What would cause it to be come loose?

    5. For DLRO, which is acceptable results?
    A)151,128,98
    B)130,101,154
    C) 157, 230, 168
    D) 68,84,98

    6. Given a circuit breaker schematic what happens after the 51 element trips?
    Click image for larger version. 

Name:	control 50-51 schematic.png 
Views:	29 
Size:	32.9 KB 
ID:	339
    A) Trip coil energizes and opens the breaker
    B) 86-1 contacts close
    C) 86-1 and 86-2 relay operates
    D) 86-1 relay operates
    E) 86-2 relay operates

    7. What is the Resistance from A to B?
    Click image for larger version. 

Name:	ductor.png 
Views:	11 
Size:	4.9 KB 
ID:	340
    A) 31 ohms
    B) 40 ohms
    C) 30.25 ohms
    D) 60 ohms

    Sorry I had to remove the remaining questions.. hope everyone got what they needed while it was up.
    Attached Thumbnails Attached Thumbnails ups synce.png  

    Last edited by cbrazzil; 4 Weeks Ago at 05:49 PM.

  2. #2
  3. burnettj1986 is offline Junior Member Pro Subscriber
    Join Date
    Mar 2018
    Posts
    4
    Reputation
    Quote Originally Posted by cbrazzil View Post
    NETA III TEST -
    Items on the last test pooled from several techs

    1. What does a bell alarm do?

    2. In the diagram where is the anti pump relay located?
    Click image for larger version. 

Name:	anit pump.png 
Views:	93 
Size:	20.4 KB 
ID:	337

    3. What is this device?
    Click image for larger version. 

Name:	network.png 
Views:	14 
Size:	1.04 MB 
ID:	338
    A) Network protector
    B) mining breaker
    C) chemical unit breaker
    D) Metal enclosed breaker

    4. On a 87 diff relay, the tap screw was found to be loose but tripped. What would cause it to be come loose?

    5. For DLRO, which is acceptable results?
    A)151,128,98
    B)130,101,154
    C) 157, 230, 168
    D) 68,84,98

    6. Given a circuit breaker schematic what happens after the 51 element trips?
    Click image for larger version. 

Name:	control 50-51 schematic.png 
Views:	29 
Size:	32.9 KB 
ID:	339
    A) Trip coil energizes and opens the breaker
    B) 86-1 contacts close
    C) 86-1 and 86-2 relay operates
    D) 86-1 relay operates
    E) 86-2 relay operates

    7. What is the Resistance from A to B?
    Click image for larger version. 

Name:	ductor.png 
Views:	11 
Size:	4.9 KB 
ID:	340
    A) 31 ohms
    B) 40 ohms
    C) 30.25 ohms
    D) 60 ohms

    8. What is not tested for an Adjustable Speed Drive System?
    A) Overload relay elements by injecting primary current through the overload circuit and monitoring trip time of the overload
    B) Primary inject the breaker
    C) Perform operational test by initiating the control devices
    D) Perform resistance measurements through bolted connections
    E) Perform dielectric withstand voltage test

    9. Select all that apply from the following, which are fiber optic connectors?
    A) RJ45
    B) 8P8C
    C) TYPE G
    D) ST
    E) MT-RJ
    F) SC

    10. With a 45 degree angle and apparent power of 500, what is you real power?

    11. What is the temperature difference that would show a possible deficiency and warrant an investigation?
    A) 40 c <
    B) 1-10 c
    C) 21-40 c
    D) 11-20 c

    12. Temperature corrected winding-resistance values should compare within _______ of
    previously obtained results.
    A) 1%
    B) 3%
    C) 5%
    D) 10%

    13. How to properly test winding insulation high to low?
    A) guard ground
    B) test high to low and then low to ground subtracting the result
    C) high to low with ground unguarded
    D) test high to low at the lower kv rating with ground guarded

    14. For microprocessor to laptops, which are the most common problem?
    A. Baud rate
    B. wrong cable
    C. Com port
    D. Technicians fault
    E. Fiber connection is cracked

    15. At what voltage is it safe to wear cotton clothing?
    A) 50-150
    B) Less than 50
    C) 151-750
    D) 75-120

    16. What is the restricted approach boundary for 13,800V ?
    A) 1ft 6 inches
    B) 2ft 2 inches
    C) 3 ft
    D) 6 ft

    17. How is the ups synced to the output V
    Click image for larger version. 

Name:	ups synce.png 
Views:	9 
Size:	12.0 KB 
ID:	341
    A) Incoming source
    B) Not determined
    C) Emergency generator
    D) Bypass source

    18. For silicone insulating liquid, what is not tested?
    A) Dielectric breakdown
    B) Viscosity
    C) Interfacial tension
    D) Neutralization number

    19. An alternator containing eight poles per phase is turning at 1500 RPM. What is the output frequency?
    20. Three capacitors, a 12 F, a 20 F, and a 30 F, are connected in parallel to a 60 Hz source. The total XC is?
    21. If a breaker is timing at 10 cycles slower than nameplate and 2nd time it is 4 cycles slower, what is the best course of action next?
    A. Operate till it falls within tolerance
    B. Spray lube on the bearings
    C. Use penetrating lube on the bearings
    D. Breaker needs to be marked bad and removed from service


    22. If the current flowing in an operating circuit must be approximately measured without interrupting the current, which of the following through type current transformers would you recommend?
    A) Bar
    B) Split core
    C) Wound
    D) Window

    24. 23. If a = (5, -12), what is the magnitude and direction of a?

    25. Which of the following protection element tests would you most likely NOT perform on a 21 device?
    A) Maximum reach
    B) Maximum torque angle and direction
    C) Offset
    D) Overcurrent pickup

    26. When arcing occurs in SF6 , what is one hazardous byproduct?
    A) Sulfur Hexafluoride
    B) Hydrogen sulfide
    C) Hydrogen fluoride
    D) Metal Fluoride

    27. What is the theoretical maximum symmetrical fault current that would be available at the secondary terminals of a 3-phase 12,470-480Y/277V, 1000kVA, 7% impedance transformer:
    a. 19,246 amperes
    b. 1,429 amperes
    c. 17,184 amperes
    d. 741 amperes
    e. 12,077 amperes

    28. What causes a white substance to form on terminals?

    29. Feeder breakers in a hospital with a 3000A 480V service that serves critical care have to have?
    A) Ground fault
    B) shunt trip
    C) zone interlock
    D) transfer schem

    30. An ATS does not transfer from utility to generator. The generator is running and producing voltage. Which of the following is the cause of it not transferring?

    A) The breaker feeding the ATS did not open
    B) battery does not have enough charge to operate the ATS
    C) Frequency of the generator is too low
    D) Service only lost one phase

    31. What device uses controls for transients for capacitor switching?

    32. Given a magnitude of 15 @ 30 degrees multiplied by magnitude 20 @ 60 degrees?

    33. R rated fuses are used for:

    A- Overload for motors
    B- Overload for XFMRS
    C- Protection for motors
    D- Protection for XFMRS

    34. 4/0 grounded cable is rated at 43kA for 15cycles. What is the minimum number of cables per phase required to safely ground a 2500kVA 5.75%Z transformer on the 480V side

    A-1
    B-2
    C-3
    D-4

    36. A utility defines their horizontal bus at the customer point as ABC left to right facing the customer with ABC rotation. The customer defines their buses as ABC left to right facing the utility but with CBA rotation. For a first-time connection the customer has to:
    A) Swap rotation at the relay to CBA
    B) Do nothing
    C) Swap A and B
    D) Swap cables at the customer bus to CBA

    37. An alternator containing eight poles per phase is turning at 1500 RPM. What is the output frequency?

    38. Which statement is correct about I2T on/off settings?
    A: Swap A & B phases and leave phase sequence alone
    B: Swap B & C phases and leave phase sequence alone
    C: Leave phasing alone and change phase sequence to ABC
    D: leave phasing and phase sequence alone

    39. With a nominal system voltage of 50-150 V, what is the restrictive approach boundary?
    A) 1ft
    B) 2ft
    C) Avoid contact
    D) Not specified

    40. What is the best way to test a removable temperature sensor on a transformer?
    A) Meter and loop check
    B) Meter and thermocouple tester
    C) Heater and Meter
    D) IR camera

    41. Best type of motor to use if it is going to be speed controlled?

    A) Shunt
    B) Induction
    C) Series
    D) Compound

    42. On a surge arrestor lead cable, what is needed in order to reduce impedance?
    A) short cable no bends
    B) short cable with small loops
    C) short cable with big loops
    D) avoid sharp bends

    43. Which oil test do you perform on HV oil switch?
    A) DGA
    B) IFT
    C) Di-electric strength
    D) water content

    44. What is the limited approach boundary for 35KV switchgear?
    A) 5 ft
    B) 6 ft
    C) 8 ft
    D)10 ft

    45. Winding results on a motor indicate possible degradation when the output waveforms show:
    A) Winding waveform symmetry
    B) Noticeable difference in winding waveforms
    C) Chopped waveforms on grounded windings
    D) Chopped waveforms on phase ungrounded windings

    46. Undervoltage protection for a UPS should:
    A) Inhibit the ATS
    B) Open the AC input breaker
    C) Start the gen
    D) Open the inverter input breaker

    47. What would cause a generator to trip on 32R?
    A) voltage higher than the utility
    B) voltage lower than the utility
    C) phase reversal
    D) overcurrent

    48. A CT supplies multiple devices. To confirm which devices are connected to it, the output of a single phase 5A source is connected to the X1 terminal of the CT without removing the existing wiring. The expected current at each correctly connected device would be:

    A) Measurable but small because most of the 5A test current would return to ground through the CT winding
    B) Unmeasurable, because the CT winding would short the test current source
    C) Between 1A and 4A with the balance of 5A returning through the CT
    D) 4A to 5A, because the CT winding impedance is much higher than the connected load impedance

    49. Which of the following statements is true pertaining to network protectors?

    A) There is no separate source of control power
    B) They use a low voltage contactor
    C) There are multiple external sources of control power
    D) They use a medium voltage contactor

    50. What is an application for a circuit switcher with a pre-insertion inductor?

    A) Transient control w/ high fault currents
    B) Transient control for capacitor bank switching
    C) Current damping at 12.4kV
    D) Current damping above 34.5kV
    you should delete this until after this testing cycle is complete

Subscribe

Login or register to leave a reply!


Share this thread

Related Topics

  1. NETA IV TEST
    By MartyCoyne in forum NETA Level 4 Exam
    Replies: 14
    Last Post: January 31, 2019, 05:47 PM
  2. NETA II test
    By dvansick2345 in forum NETA Level 2 Exam
    Replies: 7
    Last Post: January 31, 2019, 02:19 PM
  3. Who Else is Taking Level 4 in January 2019?
    By Wanderer20001us in forum NETA Level 4 Exam
    Replies: 0
    Last Post: December 26, 2018, 12:51 PM
  4. NETA II test 7/13/2016 is different
    By Bradfoxthelegend in forum NETA Level 2 Exam
    Replies: 20
    Last Post: September 27, 2017, 02:45 PM

Tags for this Thread



Related Content


Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support