Follow Us
Results 1 to 2 of 2

Maximum size conductor for 200A load break elbow

    #1
  1. J2019L is offline Junior Member Pro Subscriber
    Join Date
    May 2014
    Location
    Seattle, WA
    Posts
    7
    Reputation

    Maximum size conductor for 200A load break elbow

    What is the maximum size conductor that can be terminated using a 200A load break elbow?
    If the answer is 250 kcmil, it should be a better answer. It was very conservative solution based on NEC310.60 Table 310.16. From NEC 310.60 other tables 250 kmil was a sufficient solution but it was not a satisfied answer due to ambient temperature and number in raceway.

  2. #2
  3. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member
    Join Date
    Feb 2018
    Location
    Jacksonville, NC
    Posts
    244
    Reputation
    Quote Originally Posted by J2019L View Post
    What is the maximum size conductor that can be terminated using a 200A load break elbow?
    If the answer is 250 kcmil, it should be a better answer. It was very conservative solution based on NEC310.60 Table 310.16. From NEC 310.60 other tables 250 kmil was a sufficient solution but it was not a satisfied answer due to ambient temperature and number in raceway.
    I've never seen more than one cable per phase pulled and terminated with a 200A load break connector. Per Cooper, the largest cable termination can be made on a 1/0 awg stranded or 2/0 awg solid conductor. I would assume the answer to be 1/0.

    http://www.cmewire.com/catalog/sec15-mvs/mvs-01-amp.pdf
    https://www.borderstates.com/Catalog...1Y5015/2379792

Subscribe

Login or register to leave a reply!


Share this thread

Related Topics

  1. How to Size Transformer Neutral Resistor
    By AlexT90 in forum NETA Level 3 Exam
    Replies: 6
    Last Post: September 13, 2020, 07:18 PM
  2. Safely discharge HV feeder using load break disconnect switch (procedure)
    By SecondGen in forum Safety and Arc Flash Talk
    Replies: 3
    Last Post: August 17, 2020, 01:08 PM
  3. Expected contact resistance measurement based on breaker frame size
    By SecondGen in forum Electrical Testing Talk
    Replies: 6
    Last Post: July 11, 2020, 03:01 PM
  4. What is the theoretical maximum symmetrical fault current?
    By ryan.chapman@emerson.com in forum NETA Level 3 Exam
    Replies: 5
    Last Post: September 24, 2018, 11:41 AM
  5. Testing liquid filled transformers with load break bushings
    By GDerr81 in forum Electrical Testing Talk
    Replies: 2
    Last Post: November 15, 2016, 02:47 AM

Tags for this Thread



Related Content


Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support