    Couple NETA III Questions

    What is the expected Maximum Trip Time (in Seconds) for a 240V, 400A molded-case circuit breaker inverse time test at 300% of Rated Continuous Current?

    230

    275

    300

    350



    1000kva 34.5kv to 480v secondary transformer 5% imp. Apply 480v to primary side and ground secondary. What is primary fault current?

    8.1A

    4.65A

    5.72A

    11.95A

  2. #2
  3. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Seasoned Member Pro Subscriber
    Join Date
    Feb 2018
    Location
    Richmond, VA
    Posts
    59
    Reputation
    What is the expected Maximum Trip Time (in Seconds) for a 240V, 400A molded-case circuit breaker inverse time test at 300% of Rated Continuous Current?

    300
    This is directly from NETA/ATS Table 100.7