    What is the alternator phase current?

    A delta-connected three-phase alternator is driving a wye-connected resistive load. The alternator output voltage is 480 V. The load resistors are 12 ohms each. What is the phase current in the alternator?
    Your Answer: 13.33 A
    Correct Answer: 40 A

    The correct answer is not correct.

  2. #2
  3. Join Date
    Feb 2019
    Location
    Reno, NV
    Posts
    2
    Reputation
    Quote Originally Posted by wayneups View Post
    A delta-connected three-phase alternator is driving a wye-connected resistive load. The alternator output voltage is 480 V. The load resistors are 12 ohms each. What is the phase current in the alternator?
    Your Answer: 13.33 A
    Correct Answer: 40 A

    The correct answer is not correct.
    Agree with your assessment. My math:

    Find phase voltage of Wye connected load => 480V/ sqrt(3) = 277.128 V

    Find phase current of load => I = E/R = 277.128V / 12 ohm = 23.094 A

    Find phase current of source => current of phase = current of line in wye connection => line current = 23.094A => current of phase in Delta = current of line / sqrt(3) = 23.094A / sqrt(3) = 13.33A

  4. #3
  5. pallen is offline Junior Member Pro Subscriber
    Join Date
    Nov 2016
    Posts
    2
    Reputation
    Quote Originally Posted by kingRADi88 View Post
    Agree with your assessment. My math:

    Find phase voltage of Wye connected load => 480V/ sqrt(3) = 277.128 V

    Find phase current of load => I = E/R = 277.128V / 12 ohm = 23.094 A

    Find phase current of source => current of phase = current of line in wye connection => line current = 23.094A => current of phase in Delta = current of line / sqrt(3) = 23.094A / sqrt(3) = 13.33A
    I calculated the same Amp values as above at first. Upon review i realized that the current calculation need to be done for the current circulating in the delta connected alternator and not the wye connected 3 phase load.
    So no sqrt 3 conversion is necessary
    add the 3 phase ohm values because they are all connected too the delta alternator.
    12Ohms x 3= 36
    480v line voltage divided by 36ohms = 13.33A is the phase current in the delta connected alternator.

Subscribe

Login or register to leave a reply!


Share this thread

Related Topics

  1. Load currents in an alternator
    By JeremyBrown87 in forum NETA Level 3 Exam
    Replies: 3
    Last Post: March 29, 2019, 11:57 AM
  2. How much is the alternator phase current?
    By clayton in forum NETA Level 3 Exam
    Replies: 6
    Last Post: March 21, 2019, 05:35 PM
  3. alternator frequency????
    By lester mcmanaway in forum NETA Level 3 Exam
    Replies: 7
    Last Post: February 1, 2019, 12:05 AM
  4. 1 phase AC 115V 1 HP motor full load current calc.
    By davidb in forum NETA Level 2 Exam
    Replies: 0
    Last Post: May 2, 2018, 02:13 PM
  5. A phase-to-ground fault would primarily produce which type of current?
    By trhea@saberpower.com in forum NETA Level 3 Exam
    Replies: 6
    Last Post: January 8, 2016, 11:14 AM

Tags for this Thread



Related Content


Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support