Results 1 to 9 of 9
5,000A Magnum SB Ground Fault verification
  1. MrBolt is offline Junior Member Pro Subscriber
    Oct 2018
    Does anyone have experience doing a Ground Fault verification through a neutral CT on a 5,000A Magnum SB main Breaker with a Digitrip 520 trip unit?
    408
    Quote Originally Posted by MrBolt View Post
    Fairly standard breaker and test, what is the issue?
  5. MrBolt is offline Junior Member Pro Subscriber
    Oct 2018
    ground fault setting is 1200A max.
    I dialed it down to 0.25, and Delay @ 0.5 - but it kept tripping at 700A. I just don't understand why.
    408
    What size sensors and plug? Assuming 5000/5000, a GF setting of 0.25x should still be 1200A like you stated. What is the test setup, are you pushing current straight across the neutral CT in a switchboard? What are your phase LTPU values when ground fault is disabled?
    408
    Depending on your test setup, you may be getting a half trip if your polarities are backwards. The 0.5 time delay would allow for a little extra current over the expected 600A half trip.
  11. MrBolt is offline Junior Member Pro Subscriber
    Oct 2018
    yes 5,000A plug. pushing current from Line side of A phase, Jumper From load side of A phase to Neutral CT, and other side of CT - back to test set.
    my question is, Shouldn't 1200*0.25=300A?
    and shouldn't it trip @ 50% its current setting?
    408
    Typically ground fault settings are based off the sensor, in this case assuming 5000A would be 5000 * 0.25 = 1250A. Since 1200A is max, the trip unit will default to 1200A. My guess is that you are getting a half trip, try reversing the direction of current through the neutral CT. If that fixes the problem, verify that the CT is facing the proper direction per design drawings.
  15. Kalbi_Rob's Avatar
    159
    Below is the link to the Digitrip 520 manual.
    https://docs.natlswgr.com/docs/W1000028.pdf
    If you notice the table on page 12, for a 5000A breaker, all ground fault settings place the trip at 1200A maximum per NEC. Thus the GF trip setting is not adjustable on such a large breaker. As described above, it sounds like your CT is reversed. No trip test is placing test set leads on the line side of the breaker phase, and Neutral Ct, and the jumper across the load side phase of the breaker and Neutral CT. 50% trip test would be reversing the leads across the neutral CT. For visual reference see the below link.
    https://testguy.net/content/279-Grou...Testing-Basics
  17. MrBolt is offline Junior Member Pro Subscriber
    Oct 2018
    Thanks for the information, I didn't understand why the breaker was tripping around 600A. now it makes sense if the GF is not adjustable.
  1. Ground fault trips at half of setting
    By joenavymctest in forum P&C / Relay Testing Talk
    Last Post: March 6, 2020, 08:45 AM
  2. Zone ground fault protection. Blocking and tripping?
    By marvinray in forum NETA Level 4 Exam
    Last Post: October 6, 2017, 03:42 PM
  3. Testing ground fault reduced voltage and blocking capability
    Last Post: January 29, 2016, 02:46 PM
  4. What is ground fault blocking capability?
    By madsenate in forum NETA Level 3 Exam
    Last Post: June 23, 2015, 11:03 AM
  5. Ground fault explained with simple light circuit
    By CCooter in forum NETA Level 2 Exam
    Last Post: May 5, 2015, 09:56 AM