Results 1 to 7 of 7
Power Factor 15kV Vac Breakers
    Oct 2015
    In the NETA ATS and MTS power factor testing for a medium voltage vac breaker is an optional test. I don't believe it is a recognized test by manufacturers. Does anyone have any documentation to back this up? Is it a typical test done by others?
    329
    Quote Originally Posted by deloye4 View Post
    The Doble book mainly talks about the bushings for this test, I took a quick look through a few VCB manuals and none of them mentioned PF testing as part of maintenance. I don't know that this is a standard factory test either, other than maybe the bushings which I imagine are PF tested individually at production? As far as I know we've never done this for a customer at our shop as part of any standard service.
    Oct 2015
    These are for 15kV breakers. Manufacturers may not call it power factor tests, but that's the naming in the NETA book.
    10
    We have had customers that required it for all vac bottle breakers, we showed they where it was listed as optional but they still wanted it. Doble has standards set for most Vac breakers however we have found that very few actually pass by doble standards.
  9. CEBrighton is offline Junior Member Pro Subscriber
    Feb 2019
    PF medium voltage breaker
    Had this happen a few days ago, Power factored a medium voltage vac breaker and the test set could not recognize the leakage current because it was so low. Pretty much a pointless test.
    -Justin
  11. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Seasoned Member Pro Subscriber
    Richmond, VA
    75
    Hence the reason NETA always states test per "MANUFACTURER'S PUBLISHED DATA." I have only seen manufacturer's call for withstand and vacuum bottle integrity tests.
    Unfortunately, some customers want what they want and don't listen to reason.
    Aug 2018
    Most manufacturers do not recommend power factor on vac or sf6 breakers. Most just high pot vac breakers but there is specialty equipment that use magnetic fields to measure vacuum.
  1. Power Factor Testing
    By E-DivMafia in forum NETA Level 2 Exam
    Last Post: October 31, 2018, 02:22 PM
  2. Replies: 9
    Last Post: August 16, 2018, 02:28 PM
  3. Transformer Oil Pressure when Power Factor Testing
    By ElectricalTestTech in forum Electrical Testing Talk
    Last Post: July 10, 2018, 07:43 PM
  4. Replies: 7
    Last Post: May 28, 2018, 04:21 PM
  5. Power Factor for New Mineral Oil
    Last Post: August 16, 2016, 01:11 PM