    During the performance of an excitation current test on a power transformer, you notice that two of the currents are higher than the third reading. Why?
  2. #2
  3. Join Date
    Jan 2016
    Posts
    4
    Reputation
    Quote Originally Posted by kcorpuz View Post
    It is due to transformer core reluctance which is proportional to current. Voltage that you apply for testing is constant therefore magnetic flux.
    E(voltage) = 4.44 f*N(number of turns)*F(flux)
    Voltage must be constant to keep Flux constant. Number of turns is fixed.
    Now, N(number of turns)*I(current) = F(flux)*R(core reluctance)
    Higher reluctance then higher current and opposite. Reluctance is lower for the center leg of transformer therefore current is lower. Two legs (one on each side) have higher reluctance and therefore have higher current value.
  4. #3
  5. Join Date
    Jan 2016
    Posts
    7
    Reputation
    Quote Originally Posted by Artonic View Post
    Thank you the respond. That for sure helps a lot.
  6. #4
  7. Join Date
    Jun 2022
    Posts
    1
    Reputation
    Hello,
    I noticed that this is only true for a wye connected transformer, but not a delta connected transformer. Can anyone explain why this is?
Subscribe
Login or register to leave a reply!
Share this thread
Related Topics
  1. Replies: 0
    Last Post: September 22, 2018, 12:22 PM
  2. Total burden on current transformer
    By Sanjayo in forum NETA Level 3 Exam
    Last Post: February 19, 2016, 01:50 PM
  3. Easy way to calculate transformer fault current
    By SecondGen in forum Electrical Testing Talk
    Last Post: June 11, 2015, 06:40 PM
Tags for this Thread
Follow us
Explore TestGuy
NETA Certification Training
NICET Electrical Power Testing
Help and Support