GE SR745 Protective Relay

    #1
  1. Join Date
    Sep 2017
    Location
    Washington, DC
    Posts
    60
    Reputation

    GE SR745 Protective Relay

    I was wondering if anyone had any type of spreadsheet or formula on how to calculate the currents needed to operate different parts of a differential slope. I am looking to be able to type in a primary winding current, and have it calculate the amount of secondary current needed to trip on differential. I have contacted GE and they do not have anything and basically state that we should just trust the relay. I have had so many relays fail in the past year that I do not trust their relays.

    .2*CT diff p/u
    25% slope1
    1*CT break
    98% slope 2

    16MVA, 1200:5 primary, 3000:5 secondary, 13.8kV-4.16kV, Dyn1

    I have a spreadsheet that allows me to input Winding 1 test amps and Winding 2 test amps. Based off of those it will tell me if I will see a trip or no trip. But I want to know the specific calculated pick up instead of having to continuously change my current values in the spreadsheet to get an approximate pick up.

    Thanks

  2. #2
  3. Relay1's Avatar
    Relay1 is offline
    I use to be disgusted, now I'm just amused!
    Junior Member
    Join Date
    Nov 2017
    Location
    Central Texas
    Posts
    12
    Reputation

    Diff Spreadsheets

    Quote Originally Posted by ElectricalTestTech View Post
    I was wondering if anyone had any type of spreadsheet or formula on how to calculate the currents needed to operate different parts of a differential slope. I am looking to be able to type in a primary winding current, and have it calculate the amount of secondary current needed to trip on differential. I have contacted GE and they do not have anything and basically state that we should just trust the relay. I have had so many relays fail in the past year that I do not trust their relays.

    .2*CT diff p/u
    25% slope1
    1*CT break
    98% slope 2

    16MVA, 1200:5 primary, 3000:5 secondary, 13.8kV-4.16kV, Dyn1

    I have a spreadsheet that allows me to input Winding 1 test amps and Winding 2 test amps. Based off of those it will tell me if I will see a trip or no trip. But I want to know the specific calculated pick up instead of having to continuously change my current values in the spreadsheet to get an approximate pick up.

    Thanks
    I sent a couple of spreadsheets to your e-mail address. Hope they help!

  4. #3
  5. Join Date
    Sep 2017
    Location
    Washington, DC
    Posts
    60
    Reputation
    Quote Originally Posted by Relay1 View Post
    I sent a couple of spreadsheets to your e-mail address. Hope they help!
    Thank you. I will check them out tomorrow. I am trying to figure out this algorithm. It makes me mad that GE canít provide a tool that other manufacturers do. Iíll be back at it tomorrow morning

    Thanks again

Subscribe

Login or register to leave a reply!


Share this thread

Related Topics

  1. CL protective device cycles?
    By Havik21 in forum NETA Level 4 Exam
    Replies: 4
    Last Post: November 2, 2018, 12:36 PM
  2. Silent sentinel protective relay book by Westinghouse
    By Larry5443 in forum P&C / Relay Testing Talk
    Replies: 2
    Last Post: December 21, 2015, 12:13 PM


Related Content


Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support