Transformer Math Questions
  1. david.hatch's Avatar
    david.hatch is offline Junior Member Pro Subscriber
    Received a Pair of similar questions involving current calculations on Transformers, but I'm having trouble figuring out their math.
    A primary injection is to be performed on a transformer rated 138kV/25kV, 2500kVA, 8%Z using a 480V generator connected to the high side with the low side grounded. What is the expected current on the high side?
    a) 18.116A
    b) 12.5A
    c) 226.45A
    d) 0.787A
    e) 1.36A
    And:
    A primary injection is to be performed on a D-Y transformer rated 138kV/25kV, 2500kva, 8%Z using a 480V generator connected to the high side with the low side grounded. What is the expected current on the high side?
    a) 0.262A
    b) 0.455A
    c) 0.787A
    d) 1.36A
    487
    Quote Originally Posted by david.hatch View Post
    a) 18.116A
    b) 12.5A
    c) 226.45A
    d) 0.787A
    e) 1.36A
    And:
    a) 0.262A
    b) 0.455A
    c) 0.787A
    d) 1.36A
    For the first one:
    1. Divide kVA by primary voltage to find FLA
    2,500,000/138,000 = 18.11
    2. Divide FLA by impedance to find short circuit current
    18.11/(.08) = 226.44 A
    3. Calculate ratio for 480V and multiply by short circuit current
    226.44 A * (480/138000) = .787 A
    For the second one, just use three phase voltage in the FLA calculation:
    2500kVA/(sqrt(3)*138kV) = 10.45924 A
    10.45924/(.08) = 130.7405 A
    130.7405 A * (480/138000) = .4548 A
  5. Kalbi_Rob's Avatar
    246
    For the first one:
    Ok, that just confused me. Is the reasoning for the different calculations based on an assumption that the first question is single phase xfmr, while the second one specifically calls out D-Y?
    I thought FLA calculation was independent of single phase or three phase with FLA=(KVA*1000)/(Sqrt(3)*V(L-L)). Which as I type this would answer my confusion as long as the assumption is the first XFMR is single phase.
    487
    Sorry, I was assuming first transformer is single phase. Second is assumed to be 3-phase because of the D-Y. That is the only difference I see in the two questions.
  9. Warrengarber's Avatar
    Warrengarber is offline
    Seasoned Member
    Jul 2017
    Jacksonville, FL
    62
    I agree with the assumption of the single phase transformer, no 1.732 in calculation. If that was not the case then the two questions would have the same answer.
    That is very tricky that they would ask those two questions on the same test worded almost identically?
    You also have to pay attention to the fact that they are asking for the primary Isc and not the secondary.