    Three 1000kVA single phase transformers were connected to form a closed delta connection. If one of these transformers was removed and the remaining configured as an open delta. What is the output capacity of this new configuration?


    A) 1260kVA
    B) 1740kVA
    C) 2020kVA
    D) 2360kVA


    So, my memory of open delta configurations or faulted 3-phase delta transformers are capable of 58% of total inital power. I assume three 1000KVA transformers would combine to a single 3000KVA Delta transformer thus the 58% of that would equal 1740KVA. The answer was wrong, am I wrong somewhere in my calculations?

    Here's an link to a PE Exam review that explains where I get the 58% on question 14:

    https://www.electricalpereview.com/o...er-connection/

  2. #2
  3. Join Date
    Apr 2010
    Location
    United States
    Posts
    464
    Reputation
    Quote Originally Posted by Kalbi_Rob View Post
    Three 1000kVA single phase transformers were connected to form a closed delta connection. If one of these transformers was removed and the remaining configured as an open delta. What is the output capacity of this new configuration?


    A) 1260kVA
    B) 1740kVA
    C) 2020kVA
    D) 2360kVA


    So, my memory of open delta configurations or faulted 3-phase delta transformers are capable of 58% of total inital power. I assume three 1000KVA transformers would combine to a single 3000KVA Delta transformer thus the 58% of that would equal 1740KVA. The answer was wrong, am I wrong somewhere in my calculations?

    Here's an link to a PE Exam review that explains where I get the 58% on question 14:

    https://www.electricalpereview.com/o...er-connection/

    You are correct and the answer in the database is 1740kVA, its unclear why this would be marked incorrect. This must have been a software error, thank you for reporting. Please let us know if this happens again.

Subscribe

Login or register to leave a reply!


Share this thread

Related Topics

  1. XFMR test question - wye-delta TTR
    By dbryce89 in forum NETA Level 2 Exam
    Replies: 16
    Last Post: March 13, 2019, 06:56 PM
  2. Protection and Control / Relay Testing Forum Now Open
    By testguy in forum News and Announcements
    Replies: 0
    Last Post: July 6, 2018, 02:13 PM
  3. NICET Forum Now Open
    By testguy in forum News and Announcements
    Replies: 0
    Last Post: July 6, 2018, 01:10 PM
  4. Tan / Delta or Power Factor Testing of Dry Type Transformer
    By mask12900 in forum Electrical Testing Talk
    Replies: 1
    Last Post: January 1, 2018, 08:41 PM
  5. TVRMS2 digital link open with CB in Test Position (Epic MVT)
    By SecondGen in forum Electrical Testing Talk
    Replies: 5
    Last Post: March 27, 2017, 04:49 PM


Related Content


Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support