Results 1 to 10 of 10
Power Factor testing is least effective on which of the following?
    Power Factor testing is least effective on which of the following? My Answer: MV Cable. I challenge this question, can anyone please elaborate?
    Aug 2014
    27
    MV cable is the wrong answer because when you Tan Delta a cable it is basically another way of calculating power factor.
    Aug 2014
    Capital City
    74
    Quote Originally Posted by Kbryant777 View Post
    Agreed. Dry-type transformer is the best possible answer since you are essentially measuring the power factor of the air and there are too many variables that could have an effect on your readings.
    Aug 2014
    27
    And until recently Doble didn't have Dry Type transformer as an option when doing power factor. Now with the use of a tip up test it is a more viable test.
  9. baldscreen is offline
    Baldy
    Junior Member Pro Subscriber
    Columbus, OH
    Quote Originally Posted by AlexT90 View Post
    You didn't list the possible answers for the test question. However, my vote would be for eliminating the test on SF6 breakers. Manufacturers don't recommend them or provide any acceptable values. I haven't seen any SF6 breakers with tapped bushings. They have always been hollow gas filled.
    This test makes much more sense for oil-fill circuit breakers that did have tapped bushings.
  11. ElectricalTestTech's Avatar
    Quote Originally Posted by baldscreen View Post
    I would have to disagree with this statement. The purpose of power factoring in SF6 breakers is to detect the presence of contamination and/or deterioration of the breaker’s insulating system. A power factor test is not just for tapped bushings. There are other tests like hot collar tests that can test a bushing without taps. And even if you place the HV lead on the lug pad of the bushing and connect the ground to the tank (assuming its a dead tank breaker), perform an open breaker GST test, you are still stressing the bushing, internal support insulator, and the SF6 gas.
    I would strongly recommend that you read some of the articles about power factoring on TestGuy. They are extremely helpful and may give you a better understanding about power factoring.
    https://testguy.net/content/250-3-Ba...Factor-Testing
    Good luck!
    Depends on the test "answers" given
    In reading the various posts on this thread, I'd say you all could be right...or wrong. It depends on the selection of test answers given. Sort of a "lesser of 4 evils" type question. They could list 4 things that all have valid PF results possible, but which one is PF testing LEAST effective on.
    I could PF test my desk here and get some result....but what would it mean and am I wasting my time?
    I f*cking hate those questions........who cares if PF testing a 15kVA xfmr is a waste of time, the f-ing job specs said to do it, so we're doing it!
    Apr 2010
    555
    Quote Originally Posted by madsenate View Post
    Spot on with this. Many NETA questions are "best answer" type. Original options for this question were:
    A. Dry type transformer
    B. Oil filled transformer
    C. MV Cable
    D. OCB
    E. Voltage regulator
  17. nickhaughton is offline Junior Member Pro Subscriber
    Las Vegas
    yep
  19. dadrjka16 is offline Junior Member Pro Subscriber
    Quote Originally Posted by veracon0700 View Post
    I had selected the option of MV cable as well, only because lately in specs I have been seeing more and more the requirement to record the power factor of a dry type XFMR larger than 500KVA.
  1. Understanding power factor is easy when you relate it to beer!
    By veracon0700 in forum NETA Level 2 Exam
    Last Post: November 6, 2021, 06:41 PM
  2. Power Factor for New Mineral Oil
    By Salcama in forum NETA Level 3 Exam
    Last Post: February 22, 2020, 05:12 PM
  3. Replies: 7
    Last Post: May 28, 2018, 04:21 PM
