    What voltage does a RTU operate at
    316
    Quote Originally Posted by dadrjka16 View Post
    From my experience an RTU will have a 120V or 240V main circuit that is used to control lower voltage power supplies for the various network components in addition to any lights/receptacles or other equipment in the unit itself.
    Jun 2015
    My Experience
    The newer RTU's I deal with have 135Vdc supply power. All intelligent electrical devices (IED's) talk through network switches or serial cables DNP3.0 or MODBUS protocol. No AC or DC from IED's go to the new RTU.
    Older RTU's I've seen also have 135Vdc Supply power. Secondary voltages and currents go to an analog input card. The ratios should be set up to match the instrument transformer so dispatch sees primary values. I've seen 24V dc to input cards for statuses and alarms.
  7. Relay1's Avatar
    Relay1 is offline
    Nov 2017
    Central Texas
    12
    RTU Voltages
    In Utility Substations, RTUs are powered from the station battery banks. In the event of a total station power outage, remote communications, indication and control functions are still available. I have worked with RTU systems from 24 vdc to 135 vdc. I'm sure there are many more voltages to choose from!