Determine the approximate short circuit current available

 Jump to latest post
    #1
  1. Join Date
    May 2016
    Posts
    7
    Reputation

    Determine the approximate short circuit current available

    Using the given information, determine the approximate short circuit current available at the transformer secondary: 13,800-277Y/480V, 2500 kVA, 5% Impedance

    60,000 A
    54,500 A
    42,000 A
    37,500 A
    25,000 A


    first should be 480Y/277 not 277y/480.

    basically this would be the calculation. I= (2500*1000)/(480*1.732)= 3007.08
    z= (100/5)= 20
    short circuit = 3007.08*20= 60189

    so i would just go with the closest answer correct? and also they should fix the error on 277Y.

  2. #2
  3. Join Date
    Jan 2015
    Location
    Minnesota
    Posts
    2
    Reputation

    Agreed

    I work it out to the same answer. Seems you did it right and I would go for the closest answer.



    Quote Originally Posted by rasilva View Post
    Using the given information, determine the approximate short circuit current available at the transformer secondary: 13,800-277Y/480V, 2500 kVA, 5% Impedance

    60,000 A
    54,500 A
    42,000 A
    37,500 A
    25,000 A


    first should be 480Y/277 not 277y/480.

    basically this would be the calculation. I= (2500*1000)/(480*1.732)= 3007.08
    z= (100/5)= 20
    short circuit = 3007.08*20= 60189

    so i would just go with the closest answer correct? and also they should fix the error on 277Y.

  4. #3
  5. madMAX's Avatar
    madMAX is offline Seasoned Member
    Join Date
    Dec 2014
    Posts
    57
    Reputation
    The questions clearly states "determine the approximate short circuit current". Go with the closest answer.

  6. #4
  7. Join Date
    May 2016
    Posts
    7
    Reputation
    Quote Originally Posted by madMAX View Post
    The questions clearly states "determine the approximate short circuit current". Go with the closest answer.

    yes sir but its wrong wording that what confused 277y/480 doesn't exist, 480y/277 exist

  8. #5
  9. Join Date
    Apr 2017
    Posts
    1
    Reputation

    fault current

    Quote Originally Posted by rasilva View Post
    Using the given information, determine the approximate short circuit current available at the transformer secondary: 13,800-277Y/480V, 2500 kVA, 5% Impedance

    60,000 A
    54,500 A
    42,000 A
    37,500 A
    25,000 A


    first should be 480Y/277 not 277y/480.

    basically this would be the calculation. I= (2500*1000)/(480*1.732)= 3007.08
    z= (100/5)= 20
    short circuit = 3007.08*20= 60189

    so i would just go with the closest answer correct? and also they should fix the error on 277Y.
    2500 x 100
    1.732 x .480 x5

    250,000/4.1568= 60,142

  10. #6
  11. Join Date
    Dec 2018
    Location
    Atlanta, GA
    Posts
    26
    Reputation

    Explain the math

    Could someone explain the math a little more in depth? Never mind I was confused in Z, but looking over it again I understand.
    Last edited by Ronwilson1801; December 29, 2018 at 09:27 AM.

Subscribe

Login or register to leave a reply!


Share this thread

Related Topics

  1. Here's why you should always short a CT secondary
    By SecondGen in forum Safety and Arc Flash Talk
    Replies: 6
    Last Post: May 20, 2018, 07:39 AM
  2. ARC FLash and Short Circuit Coordination Study
    By mask1290 in forum Electrical Testing Talk
    Replies: 2
    Last Post: June 14, 2017, 08:40 AM
  3. Continuous current rating of a circuit breaker
    By mainmanmerc in forum NETA Level 2 Exam
    Replies: 4
    Last Post: October 22, 2016, 07:32 PM
  4. Is there a field test for Fuses to determine how they will perform?
    By Machine Gun Kelly in forum Electrical Testing Talk
    Replies: 3
    Last Post: April 15, 2016, 12:09 PM
  5. time current curves for fedral pacific circuit breakers
    By Herc8306 in forum Electrical Testing Talk
    Replies: 3
    Last Post: June 11, 2015, 06:52 PM


Related Content


Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support