    While Testing Earth Fault Loop Impedance at Distribution Board it was found that the value of External Earth fault Loop impedance Ze is 45ohm and hence the value of total earth fault loop impedance Zs measured at the socket outlet is also very high. In order to confirm the reading the value of Ze is also measured at the Sub Main Distribution board feeding the DB and we got similar high values.

    The value of Zs and Ze measured at different DB’s and SMDB’s found having similar values. As per standard required value of Ze shall be 0.35 ohm.

    Note:

    All the SMDB’s and DB’s are feeding from one LV Panel.
    Type of earthing system used is TN-S.
    Ground resistance of Earth Electrode connected to LV Panel is 1 Ohm.

    Can any one guide to know the reason for getting such high values????

Subscribe

Login or register to leave a reply!


Share this thread

Related Topics

  1. High Current Injection LTD Test Value
    By alexlounsbury in forum NETA Level 3 Exam
    Replies: 5
    Last Post: July 10, 2017, 11:38 AM
  2. Testing ground resistance with no earth to drive rods
    By iwanttotest in forum Electrical Testing Talk
    Replies: 2
    Last Post: February 23, 2017, 09:39 AM
  3. What is the circuit impedance?
    By Bradfoxthelegend in forum NETA Level 3 Exam
    Replies: 2
    Last Post: November 17, 2016, 03:16 PM
  4. Replies: 0
    Last Post: July 7, 2016, 08:35 AM
  5. Replies: 2
    Last Post: February 2, 2016, 01:35 PM


Related Content


Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support